A 10x10 room in a moderate winter zone needs 22btu/sqft or 2200btu which is about 650w. With a 900w heater, what is the maximum temp I could maintain with an outside temp of -5C/23F? Moderate winter zone is defined as a minimum 0C/32F.

Here are the room's construction details:

There is a 5' vinyl double glazed patio door (unknown R value). The room is facing west with another exposed wall facing south above an enclosed garage (not sure if the garage ceiling is insulated). 8' ceiling with R20 insulation under a pitched roof. Wind is not an issue here, about 150kms north of Seattle. Exterior walls are 2x4 so probably R12 insulation.

Reply to
Sam
Loading thread data ...

If it needs 2200 Btu PER HOUR at 70 F inside and 0 F outside, its thermal conductance is 2200Btu/h/(70F-0F) = 31.4 Btu/h-F. A 900 W (3071 Btu/h) heater would make 3071 = (T-23)31.4, so T = 23+97.8 = 120.8 F :-)

You might enjoy painting the south wall dark and covering it with a single layer of polycarbonate glazing with an air space to make a thermosyphoning air heater.

Nick

Reply to
nicksanspam

Run a detailed heat loss calculation, then figure out how many BTUs a

900W heater produces.

formatting link

Reply to
Travis Jordan