More explaination...
EC&M
Beyond the 2005 NEC Changes: Art. 250 Grounding and Bonding By Steven Owen, National Code Seminars
formatting link
link for article]
Code Quandaries By Mike Holt, NEC Consultant
formatting link
[excerpt - see above link for full article] Changes to 250.50 were made to clarify that, where any of the following electrodes "are present" they must be bonded together to create the grounding electrode system.
Underground metal water pipe [250.52(A)(1)]
Metal frame of the building or structure [250.52(A)(2)]
Concrete-encased foundation or footer steel [250.52(A)(3)]
Ground ring [250.52(A)(4)]
Ground rod [250.52(A)(5)]
Grounding plate [250.52(A)(6)]
The intent of the change to 250.50 (wording changed from "if available" to "are present") and the addition of the exception was meant to require the use of concrete-encased foundation or footer steel as part of the building or structure grounding electrode system in new construction (if they are present), since they are considered "present" before they pour concrete.
Randy