Electrical Code question re grounding

Aug 05, 2004 3 Replies

Situation: conductors run through conduit from service equipment to a subpanel. There is an appropriately-sized disconnect in the service panel.



Question: Does the NEC require that the equipment groundING conductor be run through the *same* conduit as the groundED (neutral) and ungrounded (hot) conductors?



I am unable to find any place in the Code where this situation is addressed, either permitting or prohibiting it, whether explicitly or implicitly.



Can anyone help?


Thank you -- guess I need to get a newer code book. :-)

According to Doug Miller :

As a general FYI, both NEC and CEC requires that all conductors for a circuit are "together". Ie: same cable sheath or same conduit or same raceway etc.

Idea being that subsequent renovations don't leave you with something really wierd. Neutral on wrong circuit. Etc.

Haywiring grounds (ie: separate grounding retrofits in old houses) is an exception that the inspector will usually permit (depending on what the other end is attached to). Ditto certain kinds of K&T fixes.

You could never do K&T techniques now, no matter what you used for wire, because of these rules.

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required