I just had a new oven installed that required a new 240-volt, 40-amp circuit. The installer used 6-gauge wire for the two hots, but smaller

12-gauge wire for the neutral and ground. Is the use of the smaller wire okay?
Reply to
Elros
Loading thread data ...

Yes

Reply to
Mark

40 Amp ckt requires #10 for the equipment grounding conductor. Built-in oven may or may not require a Neutral connection, check the nameplate or install instructions. If it requires a Neutral, I would have gone full size (#8).

Jim

Reply to
Speedy Jim

Yes.

No need. The heating elements would be 240V and thus not use a neutral. Other features such as lights, timer, clock, etc. are likely only 120V and thus do need the neutral, but certainly not a #8.

-- Doug Miller (alphageek at milmac dot com)

How come we choose from just two people to run for president and 50 for Miss America?

Reply to
Doug Miller

No. Refer to NEC, Article 250-95. The equipment ground must be #10 minimum.

He's probably OK on the neutral, though -- very doubtful that the 120V load (clock, timer, lights, etc) is anywhere near 20A.

-- Doug Miller (alphageek at milmac dot com)