Can one plug a 110v tv into a 220 v outletl without doing any damage?

Feb 23, 2022 Last reply: 3 years ago 25 Replies

Not for me. I've accidentally used 120vclips at the panel between a phase and neutral and not had anything happen.

Sometimes at peak, sometimes not.

120/208 is usually OK for 120v. 208v merely lacks a neutral, but its OK. And many panels have current-limiting fuse capacity.

for x/y, y = 2x * sin(120)

That also works with 277/480

The voltage marked on my AC outdoor unit (made in 2013) is 208/230

We wired a housing area with 120/208 because we got a good deal on a bunch of AC units that needed 3 phase. I guess anyway, wasn't my decision. But I got the angry phone calls from people whose clothes dryers took forever, and ovens heated slowly. I wouldn't put 3 phase anywhere I didn't have to (in the US) because of problems with harmonics.

I understand 120/s40 to be the "system" voltage - nominal voltage at the service.

And 115/230 (or maybe 110/220) to be the "utilization" voltage - at the equipment. Mark says his AC compressor/condenser is marked 208/230 (208 would be nominal system voltage - a violation of this convention, but I don't remember seeing 200/115).

In a "208/120" volt 3-phase system "120" should always be good for 120.

A "current-limiting" fuse is fast acting, and for high current faults melts and clears before the current reaches its first peak - the let-through peak fault current is significantly lower than with a slower fuse. Bussmann FRN fuses are common current-limiting cartridge fuses that fit in normal cartridge fuse holders.

Some large apartments have 208/120 3-phase coming in and 2 phases go to each apartment - 208/120. A 240V appliance on 208V will heat slower -

208/240=87% but the effect is squared - 75%. A relatively small buck/boost transformer can boost to 240. A 240V motor shouldn't be used on 208 unless the nameplate says 208/230.

Not obvious which harmonic problem. Some harmonics on different phases, which can be caused by power supplies, can add on the neutral instead of cancelling.

That's because that's 120V.