Lets plug your numbers into this and tell me what you get.
CFM = volts x amps x 3.412 / 1.08 x temperature rise
= 237 x 20 x3.412 / 1.08x 19
=16177 / 20.5
788 CFMYou need 400 CFM per ton so Id say your as good as it gets air flow wise. 12 CFM isn't going to mean jack shit in over all performance. You are more than welcome to look it up on a fan performance curve.
Air flow isn't causing your HP to be noisey while switching into and being in defrost.
Moving along..
3.412 BTUH = 1 watt.To find BTUH using the temp rise across a electric heat element the formula is the Sensible Heat Equation.
BTUH = E x I x 3.412
Now that you know the BTUH you can find CFM by using the formula at top
To find BTUH in heat mode;
BTUH = CFM x TD (db) x 1.08
To find BTUH in cooling mode;
BTUH = CFM x HD x 4.5
HD = total heat difference ie. Enthalpy DT measured in wet bulb across the HX. You'll need a total heat chart to get those numbers unless you post accurate wet bulb numbers in cooling I cant help.
4.5 is a constant, once again at sea level which changes with altitude. A mute point in your case.Now throw those shit equations in the trash and get to work.
Otherwise I will enjoy my morning bowl of Coco Puffs for breckfy and thank God you helped to make it possible. :)
Hope this helps.