Trane Condenser Selection - 3.1 Ton XL16 vs 3.5 Ton XL15

Jul 15, 2006 10 Replies
Saved reading
Jump to replies (10)

I'm about to get my central AC replaced and was hoping to get some opinions on sizing. I currently have a 4-ton unit that feeds 13, 6" round ducts (appx 1300CFM capacity). My house is very well insulated. I recently recieved 3 estimates from authorized Trane dealers who recommened the XL16i and XL15i models. My dilemma lies in determining the correct size of the XL16 if I were to select it. All contractors indicated that the 4-ton unit is a little large and that the existing ductwork dosent support the CFM required for a 4-ton unit. None the less, 2 of the 3 recommended 4-ton units. One of the 3 recommended a



3.5 ton XL15 or a 3.1 ton XL16 (likely because the 4 ton is not eligable for the tax credit). I agree that a somewhat smaller unit (

Think about checking into a 2-speed compressor.

1300 CFM? I doubt it. Tell me what your static is then you can decide what CFM you are running.You have done a static pressure test, havent you? Bubba

So you want to run 4 tons of A/C through ductwork that will only support 3 tons..... Who spec'ed 4 tons?? How did they arrive at that size?? Maybe you should have a complete room-by-room Manual J heat load and loss calculation done to determine just exactly what you need, then go from there.

The information you have: Three contractors say 4 tons is too large. You agree. But only one contractor recommended a smaller unit. He sounds like the best of the three. A Manual J calc would give you more info if you can find a competent person to do it. But keep in mind the results can be fudged to get the answer desired. If it were my choice with only the info you gave, I would get the 3.1 ton unit recommended by the best of the three contractors. I like my unit to run and do not mind taking some time to cool down to 75F.

Your 4-ton system with that ductwork may have only been delivery 3-ton of cooling. Did it cool okay? None the less, 2 of the 3 recommended 4-ton units, wow!

We don't know what climate you live in, but I am still betting a 3-ton unit with a scroll compressor and a TXV refrigerant control, and 4-ton airhandler will do the job! \\ Do a thorough manual J individual room calc and then do everything you can to reduce the heat-gain, and then refigure the equipment sizing. No one knows what equipment size you will end up with.

Unless you live in Florida or southern Texas I wouldn't go any higher than 14-SEER. Click the link below and read everything you can on the subject before spending your money!

- udarrell - Darrell

Proof positive that when you are snowed nicely, you accept it.

There is NO such thing as a 3.1 ton unit.