I Installed A New 95 % Furnace With A Heat Rise Rating Of 50-80 Degrees. When Checking I Found It To Be 90 To 95 Degrees. What Are The Consequences If I Am Unable To Get It Within The Specified Range ? The Blower Speed Is On High So I Cannot Increase That. Is There A Way To Reduce The Flame Or Adjust The Gas Valve In Any Way ?
What Are The Consequences If The Heat Rise On A Furnace Is Above The Rating On The Furnace
Oct 02, 2012
6 Replies
Follow replies to this discussion?
First reply
Your problem is probably due to the size of your duct system. Normally when replacing a 60 % eff furnace with a 90 % eff unit, the return has to be increased and possibly the supply ducts are to small.
Read the full replyInformation here may be outdated?
Your problem is probably due to the size of your duct system. Normally when replacing a 60 % eff furnace with a 90 % eff unit, the return has to be increased and possibly the supply ducts are to small.
A higher than normal heat rise will cause a premature heat exchanger failure, and a voided warranty. If your orig. unit was old and the eff. was around 60% and you replaced it with a 95% eff. unit you have oversized the system by approx. 25% to 30%. The result is a improperly sized duct system, restricting the air flow and increasing the temperature rise across the heat exchanger.