what is min. front and side clearance from outside breaker box to a/c unit
Oct 07, 2013
2 Replies
Follow replies to this discussion?
First reply
If you are refering to a main breaker panel, The electrical and OSHA requirement is 36". If you are refering to a disconnect box for the A/C, it must be within sight of the A/C and not more that 25 ft. away.
Read the full replyInformation here may be outdated?
If you are refering to a main breaker panel, The electrical and OSHA requirement is 36". If you are refering to a disconnect box for the A/C, it must be within sight of the A/C and not more that 25 ft. away.