Just finished self-installing a second identical Haier 3.5 kW unit, indoor AS35RBAHRA-4 with the outdoor 1U35YESFRA-4, R32 on the 510 g factory charge, short pipe run, and I'm in Spain. Handy thing is the first one heats perfectly, so I've got a working twin to compare against. On the new unit, cooling, dry and fan-only all behave, blower kicks in within seconds at every speed. Heating is another story. Louvres open, the outdoor compressor starts, but the indoor blower stays silent no matter how long I let it run, well past the 15 minute mark. Then the outdoor side keeps starting and stopping, which I guess is pressure building with no air moving over the indoor coil. No code on the display, it just shows room temperture. I've been through the obvious stuff allready. Valves confirmed open, 4 turns on the liquid and 6 on the gas before reopening, vacuum down to 60 microns with a decay of 110 to 160 over 15 minutes, soap on all four flare nuts came back clean, wiring matches 1(N)/2(L)/3(C) plus earth at both ends, the CN6 ROOM/PIPE connector is seated, swapped the remote from the good unit with no change, and left the breaker off for hours. Outdoor discharge air feels cold in heating, so the reversing valve probaly did swap over, though I checked that at night in the rain. My hunch is the pipe sensor has slipped out of its holder and is reading room air, so the logic that holds the fan back until the coil warms up never lets go. It's electrically fine, no E2 code. Does that theory hold water, or is there something else I should look at before pulling the front casing off? Genuinely curious what you'd check next.
Haier mini split: indoor fan stays dead in heating, is my coil sensor theory plausible?
Nov 20, 2026
Last reply: 10 hours ago
5 Replies
Follow replies to this discussion?
First reply
From where I sit, your sensor theory is solid, but I would not close the book on the reversing valve. Those four-way valves can stick partway into heating, and when they do the indoor coil never warms up, so the blower sits there silent while the machine short-cycles exactly…
Read the full replyInformation here may be outdated?
From where I sit, your sensor theory is solid, but I would not close the book on the reversing valve. Those four-way valves can stick partway into heating, and when they do the indoor coil never warms up, so the blower sits there silent while the machine short-cycles exactly like you are describing. I have seen that failure mode before, and it hides behind the same no-error-code face you are getting.
The cold discharge air you felt is a hint, not proof, given you checked it at night in the rain. Feel the thick pipe at the service valve instead. If it gets hot within seconds the valve has committed and your attention shifts to the pipe sensor. If it stays cool, the valve is stuck. Either way, the fan itself is almost certainly fine. These units deliberately hold the indoor blower off until the coil sensor reads roughly 40 to 50 degrees, so a sensor that has slipped out of its clip and is sniffing room air would explain everything, including the outdoor cycling.
Following this one closely because I'm only just getting my head around these units myself and I'll be hanging my first split soon. One thing I keep wondering reading your setup, that working twin of yours is a handy reference. When it first kicks into heating, does it also sit with the blower off for a while until the coil warms, or does air start moving pretty quick? If the good one holds the fan back too, then the waiting part is normal and the new unit just never gets there. I have no feel for what counts as a long wait on these though, so if anyone knows roughly how long is normal before calling it a fault I'd love to hear it.
Agreed with the sensor side of this, and that working twin is doing a lot of heavy lifting for you. When I did my own split install I second-guessed every connection and ended up photographing the wiring twice just to sleep at night, so I know the itch of wondering if it's you or the machine. What you describe reads like a control decision rather than a blower fault. The unit won't release the fan until the coil reads warm, and a sensor that has slid out of its holder just sees room air forever, which also explains the outdoor unit cycling. When you get that casing off, let us know if the clip had actually let go.
One pedantic snag for me is the vacuum wording, because a test that ends at 110 to 160 microns after 15 minutes is a rise rather than a decay, unless you have phrased it loosely and the readings actually fell to that range. Either way the clean flares and working cooling mode make a real leak unlikely, so I would not chase it, but it is the sort of thing that reads differently a week later. How did you measure it, gauge reading at the end compared with the starting point?
Beginner here but the whole thing reads to me like the machine is being told the coil is cold when it isn't, which matches what most people are saying about the sensor. I did wonder about the outdoor unit stopping and starting though. How long does it actually run each time before it shuts off, like a couple of minutes or closer to ten? That might narrow down which problem you've got. Also when you do take the cover off I'd be curious whether the little sensor holder is something obvious once you see it, or tucked away somewhere fiddly.