Testing ring circuit

Hello,
After finally finishing my new kitchen circuit I would like to check if the continuity of live, neutral and earth to determine if they do indeed complete a ring.
Searching on Google I have discovered continuity testing but with this it seems you need to test each stage separately.
What I would like to do is to simply remove one socket cover, disconnect the wires and test that each wire completes a ring.
Is this possible, if so what type of kit do I need to perform this. A Screwfix link would be excellent!
Thanks,
John
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

the
the
Go to your Consumer Unit (main fuse box) and switch it off. Remove the two red insulated cables from the breaker and connect your meter over them. Set the meter to read the Ohms ranges and it you should have a reading of between 3 and 10 Ohms depending on the length of the cables in the ring. Repeat this for the black insulated cables and the earth connecting centres and you should find out if all sockets are connected together.
If you don't get a drop in the Ohms range on any of these test, then you have a break somewhere in the circuit and you'll need to test from each socket to the next to find the break.
Hope this helps a bit.
--
www.basecuritysystems.no-ip.com
Outgoing mail is certified Virus Free.
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

if
disconnect
--
www.basecuritysystems.no-ip.com
Outgoing mail is certified Virus Free.
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks Big Wallop

this
A
the
them.
ring.
you
each
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

It would, although is quite expensive if all you need is a basic DVM. Maplin sell ones which will do this job for only a few pounds.
Also, if you go to eBay 'Test Equipment' you'll find a new DVM on offer that also does temperature, which is very useful for balancing central heating or checking ovens etc. They sell for about 15 quid, and IMHO are good value.
--
*The more people I meet, the more I like my dog.

Dave Plowman snipped-for-privacy@argonet.co.uk London SW 12
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Although this will give you an indication of the connection, it isn't actually good enough for the regs. You'd need something more like:
http://www.tlc-direct.co.uk/Products/TM9054.html
These meters will apply up to 200mA to give a much more reliable indication of resistance and will give 2 decimal places of ohms. Obviously, this isn't the sort of price range you're looking for to test one circuit. To fully test a circuit, you need one of these (which also does high voltage leakage testing) an earth loop impedence tester and an RCD tester.
I wouldn't be surprised if you can hire from HSS, or you can just use a multimeter and hope, but you won't have complied with the regulations. Last I looked, the going rate on eBay was 50-100 for each digital meter.
Christian.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
"John Greenwood" wrote | After finally finishing my new kitchen circuit I would like to check if the | continuity of live, neutral and earth to determine if they do indeed | complete a ring. | Searching on Google I have discovered continuity testing but with this it | seems you need to test each stage separately. | What I would like to do is to simply remove one socket cover, disconnect the | wires and test that each wire completes a ring.
As well as testing for ring continuity you have to check for inadvertent bridging of the ring.
http://www.tlc-direct.co.uk/Book/8.4.2.htm
describes a procedure
Owain