Hi.
Im commissioing a new installation on a project in wherby the repository / bookstores have to be kept at 16 DegC and 55% RH.
Now then, the rooms are sealed and have a door mounted pressure relief. duct.
We are supplying the rooms with 95% recirculatedair 5% is conditiond fresh air makeup. We are allowing for 5% losses through the relief duct in an effort to keep the space positvley pressurised.
The fresh air make up runs through an ahu with the following (essential only) components, Frost battery, Cooling Battery, Heater battery, steam humidfier.
External air comes in at this time of the year at around 22 DegC 78 % RH.
This fresh air (5%) is supplied onto the recirc air handling units serving the repository.
The repository units contain 4 coils and a humdifiers.
cooling, heating, for sensible load and then cooling / heating for latent load.
The units have been running for a month but i cant get the %RH level in the spaces below 60% it should be 55%.
The return air coming back is at 16 DegC (therfore is at setpoint) and the humidity is at say 67%.
We are controlling the coils on return air and therfore as you can see there is a demand for dehumidification.
The secoond cooling coil actuator (latent load) has wound fully open in an effort to do this, this drops the temperature off the coil to 7 DegC. Therfore the reheat coil comes into heat it back up to the required calculated setpoint this fluctuates depending on the extract air deviation from the room SP setpoint which has settled out at 15.7 DegC
Anyway the % RH off coil is around 95% and following the reheat it only drops to 70% it appers as though the air isnt any dryer.
Ive worked it out pyschrometricaly and although the RH hasn't change the moisture conent has. But the consulatnt isnt intrested in moisture content only RH I have no idea where to go from here. it should be noted that the sensors we are using are specialist and have been pre calibrated. I have checked there positions and redings whilst point to point commissioning. Also the coils in the ahu have correct pipework portings and the coils are positioned in the correct way. Finally the steam humdifier remains isolated.
Any suggestions will be appreciated.