Electric shower

Page 1 of 2  

I had an electric shower, rated at 7.5 KW, put into my bathroom around 10 years ago. IT was on its own fuse box with a 30 AMP fuse. I replaced the shower 2 years ago and took advice which was to keep the shower under a 10 KW rating. My new shower is now 9.5 KW. I have had to replace the ceiling switch and had a qualified electrician do this last year. Every thing has been fine. All of a sudden the fuse has blown on two occasions in the same day. Can someone explain what maybe the problem. Is the fuse too small and if so why has it worked for a year without a problem? I noticed on the fuse packaging that a 45 AMP fuse should be used for a 9-10KW shower, but I am surprised it has worked for this long. If it is the case that the fuse is too small do I need to new fusebox as a 45 AMP fuse will not fit in the box I have? Would a circuit breaker be a better bet? Any help would be greatly appreciated.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

(10000/240) so it's little surprise your fuse is blowing. If it's only just started blowing then perhaps your local supply voltage has risen recently maybe from 220 to 240 perhaps, remember 10KW is not a constant, it all depends on the voltage and current (V x I) and I depends on the resistance of the element and the voltage (I = V/I). Also it's possible your only now using your shower on full power due to the time of year. Incidentally you should be using 10mm cable for a 10KW shower check that 6mm wasn't installed for your smaller shower as this cable is only rated at 32A.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Whilst I agree that 10mm is the the best solution, 6mm cable is rated at 32 amps on the worst case scenario when inside conduit inside insulation. If the cable is clipped direct or clipped and plastered over then it should carry 47 amps.
What is more worrying is a 30amp fuse blowing when 40 amps is been drawn. The fuse should withstand 45 amps for one hour before blowing. Either the shower is on its way out or there is some damage to the cable. The OP did not state how long the shower was running before the new fuse blew.
Adam
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Adam it's in his house so it's going to be method 3 isnt it in all proberbility, ie installed directly in an insulated wall. It's not going to be clipped direct and remember you need to size for the worst part in the circuit. 6mm for a 10Kw shower? It would hardly be professional to say this is ok
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Too many probables. We have no idea how or where the cable runs. I would have said if the cable is installed directly in an insulated wall then it is installation method 15 not reference method 3 (3 may be OK but 15 would not be), but there is also a good chance the cable is embedded in plaster which case use reference method 1

I never said it was. We are refering to a 9.5kW shower not a 10kW shower. If the shower is 9.5kW @ 240 volts (another unknown) and if the cable is clipped or embedded in plaster the cable and then passes through some insulation then table 6B applies and the cable may still be sufficient.
Adam
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Yes sorry, typo, I was looking at the cores box instead of method box.
(3 may be OK but 15 would not

I've always considered embeded in plaster as thermal insulation. Method 15

6B? I know there's a 6B dealing with trenching, underground cable and cables alonside railway lines etc. What do you mean?
I would have stuck with 4D5A but then as you say there are too many unknowns

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@bobwatkinson.wanadoo.co.uk says...

sure that someone sometime would want to fit a more powerful unit.
--
Roland Butter :- There\'s nothing like a knob of butter.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Zinzan wrote:

7500 W / 240V = 31.25 A
9500 W / 240V = 39.58 A
When you are putting in a shower you need to ensure that the fuse will melt before the wire melts, and that the fuse and the wire are both "thick enough" to avoid melting under normal use.
I reckon that either the shower is drawing more power (perhaps due to colder water coming in over the winter), or the wiring is buggered, causing increased current and the fuse to blow.
If possible, I'd put in a 45A fuse and possibly re-run the job with thick wires.
I'm not an electrician BTW.
John
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

No that can't happen. A resistive element simply works or it doesn't. It can't react to water temperature diference and adjust the output to achieve the heating effect. The OP may select the hotter setting if the water is colder though. This would add additional elements creating a higher current.
or the wiring is buggered,

agreed OP must check the cables are 10mm not 6mm or go back to a 7.5KW shower

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

along in a bit to put me right if I'm wrong!
--
Roland Butter :- There\'s nothing like a knob of butter.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
says...

bring us into line with Europe. The tolerance however is +- 10% of 230V or 216.2V - 253.0V. In reality the voltage didn't really change only the nominal voltage 'tag' did.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
I should of course have said 207V not 216.2V. These changes came into effect in 2003. Prior to this it was 240V +- 6%
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

We are on 230V +10% to -6% according to the supply note on a new intall I fitted today.
Adam
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Hi guys,
Thanks for the comments. The cable is 10mm and is in a conduit embedded in the wall. When I replaced the shower two years ago I was told that I would be OK if I kept the new shower below 10 KW hence the reason I went for 9.5 KW. The surprise to me is that has worked fine for over a year since I last replaced the fuse. Why would it all of sudden decide to blow fuses?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

mentioned. The increased current doing the damage.
Theory 2. you may have a faulty shower
Theory 3 you may have faulty wiring
get the above checked but with 10mm cable there is no problem uprating your fuse if you physically can
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Are the fuses going with a big bang? If so I would suggest a faulty shower or a damaged wire.
Adam
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Hi Adam
The fuse box is downstairs from the shower but there has been no noise when it does blow. When I replace it the old fuse is just a but hot. I am getting an electrician to look at it so hopefully he will get to the bottom of it. It always seems to be at this time of year as it did it last year at this time and the year before. That is why I suspected that it may have had something to with the water temperature that is feeding the shower. Today was a milder morning and everyone in the house had a shower successfully without the fuses blowing. It beats me what is going on, but hopefully the electrician will get to the bottom of it.
Billy

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@bobwatkinson.wanadoo.co.uk says...

reduce power consumption.
--
Roland Butter :- There\'s nothing like a knob of butter.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
says...

No way. If they dropped the voltage they drop the power. That means they also drop their income from us bill payers. They ain't gonna go for that. Interestingly though their are manufacturers now rating appliances at 230V. This means that in a lot of cases they are running over powered. A 3KW fire may be running at 3.25Kw foe example.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Roland Butter wrote:

Hmmm.
7500W / 240V = 31.25A
7500W / 230V = 32.61A
So that's more current for the same power!