I have a 100 Amp supply into the house and at peak use we maybe get to 25 Amps in the house. No electric showers or hob.
I want to take a 40 amp supply to the garage via a 10 sqmm three core SWA cable around 30m long buried for 20 mtrs.
Please advise if I am getting this correct.
As I will have a car lift it needs a 32amp type D mcb in the garage.
At the house consumer unit the swa is earthed to the consumer unit as well as using one of the conductors to run the earth. The house consumer unit mcb for the garage will be 50 amp type D. It will be on the earth leakage side of the house consumer unit.
At the main garage consumer unit, SWA will not be connected. The three conductors will be connected phase, neutral and earth.
The lights in the main garage will be on the non earth leakage side of the garage consumer unit. The following will be connected to the earth leakage side of the main garage consumer unit.
Sockets 32A mcb type B with max load of a compressor 10 amps.
Car Lift 32A mcb type D, 25 amp at start up but load while lifting 15 amps. So only used for a two minutes at a time.
Heating 32A mcb type B with at max a 20 amp load but very well insulated garage so hopefully 10 amps most of the time.
Garage 2
This is half way between the house and main garage. At most lighting and a compressor. Max load 12 amps usually nearer 0.5 amps.
Lights on garage 2 non earth leakage side of garage 2 consumer unit. Sockets in garage 2 on the earth leakage side of garage 2 consumer unit.
The 15mtr long 2.5 sqmm SWA three core cable will not have the SWA connected to earth at garage 2 consumer unit but will have at the other side. It will be buried
It suits me better to take the garage 2 supply from the main garage rather than the house consumer unit. I assume it should be fed from the earth leakage side of the main garage consumer unit. A 32 Amp type B mcb.
Comments please.