What size of sub-main cable and fuse for granny annexe?

Anyone advise what size of cable is required for a sub-main going to a granny annexe? The Annexe/flat has an 8kw electric shower, a 4.5kw cooker and the usual aray of kitchen appliances. Will 10mm² twin-core and earth be adequate? It'll need it to pass the part-p certification periodic test.

And what size of main fuse is suitable for this sub-main?

Thank you,

DaveH

Reply to
DaveH
Loading thread data ...

There's no such thing as a Part-P periodic test. You'll need either a Design, Installation and Inspection and Testing Certificate, or a Minor Works Certificate, OR a building control application to the local council.

If it's a bedsit type annex, integral to the house, with gas or other non-electric heating, I'd suggest a 60A supply using 16mm.

For anything larger or if electric heating, treat as a separate dwelling and provide 100A using 25mm. If the annex might ever be used separately (rented out) then it might be worth biting the bullet and getting a new supply from the street mains.

Be aware that T&E may not be acceptable with its reduced earth conductor size, and submains are often done in MICC or armoured.

Owain

Reply to
Owain

On Tue, 17 Apr 2007 17:40:55 +0100, DaveH mused:

The size on the cable depends on the length, installation method, load etc... You have only given part of the information.

Part p isn't a periodic test. Who is doing the commisioning and certification of the installation?

10mm does sound small though, I wouldn't use it as a submain for a flat with electric cooking and heating.
Reply to
Lurch

16mm T&E with a seperate 10mm earth seems normal in new build flats around here.

Adam

Reply to
ARWadsworth

The length of the sub-main cable will be 8 mtrs.

Haven't decided yet.

The flat would not normally have any electric room heating as it has central heating.

DaveH

Reply to
DaveH

Seems worth thinking about.

OK, many thanks.

DaveH

Reply to
DaveH

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.