Tracking RCCB nuisance tripping

Sep 12, 2006 22 Replies

The voltage measured will be a function of the loading on the circuit at any given time. I have a feeling this particular test may just confuse things....

And switching the breakers off will ensure the same zero loading on all circuits.

NT

Bear in mind that leakage currents will not necessarily add arithmetically. E.g. your 2 mA from the washing m/c (which seems a bit high) is likely to be capacitive and will add in phase quadrature to any resistive leakage current present. So 5 plus 2 makes 5.4 in this case.

Classic intermittent fault behaviour to a tee...