Due to total ignorance, but seeing a reference to them on here, I looked up the Part F regulations on the OPDM site.
If I have this correctly, the Regulations require a Minimum Ventilation Rate of 0.3 l/s (litres per second) of fresh air per 1 sq m (square metre) of total floor space in a priivate dwelling.
My smallish semi is approx 6m x 5m over two floors, for a total of 108 sq m. This gives a MVR of 0.3 x 108 = 32.4 l/s.
Now, in one hour this represents 32.4 x 3600 litres of air.
The Specific Heat of Air at 0 degC is 1000J/kg-K (joules per kilogram-Kelvin) at constant pressure, and its density is 1.29 kg per cu m.
So in one hour 32.4 x 3600 x1.29/1000 kg of fresh air are required to enter the property. The 1000 comes from the conversion of litres to cubic metres. This is 150.5 kg of air.
For the sake of argument, if the external air temperature in the winter quarter is 0 degC, we need to warm this air to say 20 degC.
So, 150.5 x 20 x 1000 J are required each hour, which comes to 3.01 MJ.
But this air requires warming 24 hours a day, as the ventilation required is 24 hours a day.
So in one day we will need 3.01 x 24 MJ, and over the winter quarter this translates into 3.01 x 24 x 90 = 6500 MJ, or in familiar units,
1805 kWh of energy.Over the winter quarter I currently consume 6000 kWh in gas. I will be required now to increase that to 7805 kWh, at an extra cost (at
*todays* rates of £38; much greater next year.It kind of makes the Insulation and Boiler-efficiency regs look kind of tame.
Now, even I can spot the approximations in this calculation; but I get the impression that all these wonderful regulations are beginning to trip over each other.
In addition, anyone living in an open-plan house with this kind of air-flow rate will need to wear fur-lined boots and a warm top, and set the gas-fire to "stun".
Any comments?