>Can anyone shed any light on how much of a problem the above issues
> >are and how pumps are rated?
The Keston 130 quotes a minimum flow rate of 50l/m (0.83l/s as Grundfos
> quote it). If you download the product data for the pumps you mention (big
> pdfs I'm afraid) you'll see that the 15-60 just can't come close to shifting
> that much water but the 25-55 should be ok for heads of less than 2.5m.
Thanks - having read the manual again last night I was planning to look this up based on flow rate so you've saved me the effort. They dont make things easy do they?
Are hearing signs of low flow - localised boiling when the boiler is at full > power?
It's a noisy beast so i very much doubt i'd hear it above the fan. However, it does seem to short cycle which is likely to be related. The boiler has a pump over-run facility which can be wired out of circuit (and of course has been) so a minor rewire would probably solve the localised boiling i think i can hear when the boiler switches off.
In short, I think your man is right about the pump :-(
I'd come to the same conclusion (he was from Keston after all and wasnt interested in actually doing the work) but am wondering about the relative costs of getting the pump replaced now (when we've a lot of other expenses) versus shortening the life of the boiler slightly but not having that cost for some years.
> btw: On the bypass pipe being too small, unless it is microbore I doubt it,
> since the minute the loop goes on bypass, the boiler return temp will rise
> causing the boiler to throttle back meaning that the bypass loop never has
> to handle full power flow IMO. What size is this pipe?
the out and return pipes are 28mm (huge) for about a metre, then reduce down to, i think 22mm down under the floor into a loop of about
3m total length but a small section (maybe 20cm total ) of the loop near the pump is 15mm (again estimated). If we had the pump replaced that small section could go as well.
I'm assuming you
> have an automatic bypass valve in use.
You've lost me there - what would it look like and where would it be?. The system is plumbed in as S plan i think - seperate motorised valves on the DHW and CH, pump runs when either valve is open.