OOI, is there any reason I can't use the neutral incomer as an alternative to "Supplier's main earthing terminal"?
If there is a small residual voltage on the neutral, swapping the transformer phase and taking the average of two measurements would help but should be a fraction of 24V.
Didn't find your answer? Ask the community — no account required.
P
Pat Pending
Yes, that's correct.
I might try that, I think I have a 24v transformer somewhere.
However, what do you think about this idea for getting a more accurate Ze measurement? My loop tester has an iec connector for a mains input - a type I have plenty of - and no other leads. I get a spare lead and chop the plug off, strip the insulation back and fit a crop clip to the earth lead and a probe to the live lead.
With the supply turned off at the CU and the earth input disconnected I then connect the croc clip to the (disconnected) earth and the probe to the input side of the main switch. Would this give me a true Ze reading, or is my thinking incorrect (would I need to connect the neutral as well?)?
J
John Rumm
I would not fancy it ;-) Remember neutral is a "live" wire - it could be several volts[1] away from local earth, and can supply reasonably significant current in some circumstances.
[1] Or possibly more depending on the load being applied to it locally (by yours and neighbouring properties), and distance from the substation etc.
J
John Rumm
If its anything like my old Megga LT5, then I think it uses the neutral to power itself since it has no battery. However in principle, you could lash up something to allow it to be powered, and also have a wandering earth lead for connection to your electrode.
P
Pat Pending
That's what I'll do, I think, connect live and neutral to the input side of the (switched off) main switch and connect the earth lead to the disconnected external earth lead. That should give me a more accurate Ze.
F
Fredxx
Several is less than 24V. I am aware that neutral is now considered 'live' so best to take care.
Which should be taken into account if averaging in-phase power and reverse phase currents.
The resistance ought to be a fraction of the local earth-spike resistance. Either way it gives a worst case scenario of true live conductor to local earth resistance and prospective earth fault current.
Or am I wrong?
J
John Rumm
No, you will get a reading...
All in all though it seems like more hassle than using a bit of pipe stuck in the ground though!