Interfacing a generator to house electric's question.

Hi all, Some time ago I picked up a 7.5KVA generator complete with auto start control panel. I feel it is about time I wired it up to the house. I rewired the house, 4 bed plus annexe, some years ago and feel relatively confident in being able to interface it to the CU. Talking of the CU I'm contemplating putting in a second one so that I can have maintained and none maintained circuits. All of the lighting but only some of the power. This should ease the load on the contactor that switches between the boards feed and the genny. My questions are:-

Am I OK in using a two pole change over contactor, common to house, n.c. to board and n.o. to genny?

Any ideas on a reasonably priced contactor and what sort of current rating? I've seen a few advertised and obviously the higher the current the higher the price! As it will not be providing a circuit for the electric shower would I be OK with something around 40A rating, bearing in mind the second CU?

What should I do about the earth? TN-S at the moment. Will it be necessary to switch this, I suppose with a multiple number of faults it could be remotely possible to back feed this to the boards earth. I don't really fancy switching it if I don't have to though. Would I be OK just connecting one side of the genny output to N and earth? Should I then provide a local earth?

The genny will be 40 feet or so from the CU, any thoughts on cable?

Should I just go out and buy a box of candles instead?

Thanks for any and all comments, I've already taken a look at the ukdiy FAQ but only found one minor reference to generators.

Reply to
Bill
Loading thread data ...

With 7.5kVa this might not be necessary

yep

7.5kVa @: 240v = 31A, I'd go with 40A

you will need a local earth

If youre not sure, then yes. The only point to doing al this is if theres a good reason to do it. And there usually isnt. If you can think of nothing better to do, I suggest a life re-evaluation time.

NT

Reply to
meow2222

Check back in this group on google. This has been answered in some detail before, and it's non-trivial.

Reply to
Andrew Gabriel