Despite extensive googling, there seems to be nothing that tells me how much current flows along wires on a national grid pylon. They only list voltages. Anybody know?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Well it depends on the load one supposes. It also then depends on the voltage on thewwires as the whole idea of using high voltages is to reduce losses due to disipation when the system is under load. The answer basically is there is no answer. Might find more if you asked the max current of the one at xx to yy. Brian
--
From the Sofa of Brian Gaff Reply address is active
Remember, if you don't like where I post
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Saturday, 18 March 2017 00:07:59 UTC, James Wilkinson Sword wrote:

A 400 kV National Grid circuit may carry 1 kA in each of its three phases, thus transmitting a power of 700 MW. A 132 kV distribution circuit may carry 300 A in each of its three phases, thus transmitting a power of 70 MW. An 11 kV distribution circuit may carry 150 A in each of its three phases, thus transmitting a power of 3 MW. A 400 V final distribution circuit may carry 200 A in each of its three phases, thus transmitting a power of 150 kW.
(Remember, these voltages are phase-to-phase voltages, the phase-to-earth voltages are 1.73 times lower. Thus (400 kV/1.73) x 1kA x 3 = 700 MW.)
http://www.emfs.info/what/terminology/ (site maintained by National Grid)
[Pylon type] L12 is effectively the L6 replacement will take twin conductors up to 850mm2, but all aluminium conductor rather than the heavier steel cored kind formerly used.
http://www.gorge.org/pylons/structure.shtml
Owain
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 3/18/2017 11:18 AM, snipped-for-privacy@gowanhill.com wrote:

And Supergrid pylons (400 and 275 kV) are normally double circuit, aren't they? Three wires on each side of the "tree".
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote wrote:

200A per phase at 400V (240V phase-to-neutral) doesn't sound very high. We have a 60 A "company fuse" and I presume our neighbours do too. With an electric fire (3 KW), an electric shower (maybe 8 kW) and an electric oven and hob (maybe 6 KW), you'd be getting towards that limit but still remaining legal. Now imagine lots of people roundabout doing that. It doesn't take many houses to run up 200 A - or a total of 600 A across all three phases. How many houses are typically fed from a single feed from the substation or 11 kV-to-400V pole-mounted transformer? What is the average current that is assumed per house when sizing up the number of houses that can be fed from one substation circuit? I presume it not the full 60A of the company fuse rating.

How much of the route from the power station to the consumer is redundant multi-circuit? At one point, typically, does it change over to a given house only being fed by one set of wires, and if that line develops a fault there is no backup circuit?
Is there a backup route as far as the final substation that transforms to 11 kV or 400V, or is it higher up the chain?
I presume for maximum redundancy they try to use feeds from different places rather than two sets of wires carried on the same pylons, in case an accident takes out *all* the wires (both circuits).
I'm intrigued at the way house gets its electricity supply. There is overhead mains on wooden poles (originally four separate wires, now a single fat cable with four wires) and our house is the middle house of two adjacent blocks of three houses. There is a single feed from the wooden poles to the end of one block, and then four wires running along the back of one block, overhead across the gap to the next block and along there, with each house taking its feed from neutral and one of the three phases - I think no two adjacent houses are on the same phase. I suppose this is less unsightly than every one of the six houses having its own single-phase feed from the street poles.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
"NY" wrote in message
<SNIP>

They always used to rotate phases down a street, so (say) phase 1 -> house 1, phase 2 -> house 2, phase 3 -> house 3, then phase 1 -> street lighting, phase 2 -> house 4 and so on down the road to balance the load between phases.
We have the 11 kV to 415 v transformer on our land and are the first 'drop' of single phase at the farmhouse, but also take the three phase into the barn at 160 amps per phase. No street lighting though round here. The 11 kV can be fed from two points - we have an overhead HV line and an underground HV cable, but normally only one is active.
Andrew
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Andrew Mawson was thinking very hard :

So as to as best they can, balance the load on all three phases, so as little current as possible appears on the neutral line.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 18/03/2017 15:57, Andrew Mawson wrote:

Yep, and it's not uncommon to see that in multiples of houses. So you may have 4 houses next to each other on phase one, the next 4 on phase 2 etc.
A far more common variant (on properties built in the late 1960's and early 1970's) is house 1 and 2 on phase 1, house 3 and 4 on phase 2 and house 5 and 6 on phase 3.
--
Adam

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I wonder if anyone's ever borrowed their neighbour's electricity when theirs is off, only to find it coming back on and joined phase 1 and 2 together with a big bang?
--
If you feel tired, pull off at the motorway services -- Highway Code, UK.
How's that going to help?!?
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I think they stopped doing that many years ago. There's a small development of 26 bungalows near us - built about 30 years ago - all on the same phase.
--
from KT24 in Surrey, England

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I guess it doesn't matter how many on each, as long as it's even on each substation.
--
"Whoever said the pen is mightier than the sword obviously never encountered automatic weapons."
- General MacArthur
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 18 Mar 2017 12:05:12 +0000, NY wrote:

It's called Diversity. The DNO's know that everything will not be plugged in at the same time, so their network will cope for the vast majority of the time (and time has proven this, as there are very few blackouts caused due to DNO substation fusing blowing).Short term overloads dont stress the system too much, as can be seen on christmas day - when 50% of houses have their ovens on etc - but 50% of them are gas,then the oven is not on full power apart from the first 5 minutes, so the load isnt as much as you think I was told the typical demand for each house when the network is designed is around 5 to 10 amps.That'd give 120 houses to one substation feed at 5 amps - that seems about right.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 19 Mar 2017 07:19:45 -0000, wrote:

All very well as long as there's a suitable fuse. But when diversity is used in case of say a double mains socket in your house only taking 20 amps, but the fuse protecting it is 30A, you get fires.

5A maximum I assume. If you use 5A on average, you'd get a very big electricity bill.
--
Two blondes living in Oklahoma were sitting on a bench talking, and one blonde says to the other, "Which do you think is farther away... Florida or the moon?"
The other blonde turns and says "Helloooooooooo, can you see Florida ?????"
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 18/03/17 12:05, NY wrote:

Course not. Average power per household is 1-2KW.

Typically 11KV is run as a ring - it is here anyway, so the only single point of failure is the 240V stuff from the local substation.

As I said, round here 11KV is a ring.

--
Those who want slavery should have the grace to name it by its proper
name. They must face the full meaning of that which they are advocating
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Out here in a North Yorkshire village there seem to be 11 kV spurs, each with a pole-mounted transformer to step down to 240V. Where I'm sitting I can see the end of the 11 kV line and its transformer. Its 240V cables go underground to houses on one side of the road (probably built in 1950s) and then come above ground to 3-phase 240V overhead wires to the houses on the other side of the road (1930s).
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
NY has brought this to us :

Are you sure it is 11Kv - more likely it will be 3.3Kv.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Ah, I wasn't aware that there was an intermediate distribution voltage between 11kV and 240V. Are most power lines on pairs of wooden poles with big glass insulators and pole-mounted transformers 3.3 rather than 11 kV?
This is the pole
https://s22.postimg.org/n6x2dkkip/IMG_0456.jpg
I hadn't spotted the four horizontal wires in the foreground. I was wrong: the 240V evidently goes underground to the back of just one terrace block and then 3 phases and neutral runs between the three terrace blocks, with alternating phases - same as in our older terraces on the other side of the road from the 3.3 kV.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Wonder if H Bloomfield did a typo and meant 33Kv which is used frequently . The supply to our farm was be 11Kv , where we are now is also fed by 11Kv so to say it is more likely to be 33Kv or 11Kv would need access to official records but also where you are gives a bit of a clue, a few houses and a farm out in the sticks 11Kv but a more densely populated area with some industry 33Kv. There is some distribution done at a lower voltage usually in towns and nowadays at 6.6Kv but some supplies that have been in place since the 1920's or 30's may been slightly lower before things got standardised.
G.Harman
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I wondered that too but don't know enough about power distribution.
When I first saw this thread title, however, I assumed it was talking about how much leakage there was to earth from a pylon.
--
"That which can be asserted without evidence, can be dismissed without
evidence."
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I thought it sounded a little ambiguous when I wrote it. Probably quite a bit, as if its raining, you can even feel it coming through the air.
--