Anyone have any pointers to hot water cylinder heat exchanger efficiency data?
I will probably have a new boiler installed in the spring. I will retain a vented hot water cylinder. I am looking at dual temperature boilers with weather compensation, which adjust the flow temperature and have hot water priority over central heating.
I am trying to estimate what the worst case time is to reheat the hot water cylinder during which there will be no central heating. A naive calculation with 18Kw output boiler and 100 litre hot water cylinder raising temperature by 50 degrees suggests:
reheat time = 100 * 50 * 4190 / 18,000 seconds
(the specific heat capacity of water is 4190 J/Kg/K)
which is about 20 minutes -- probably acceptable considering only a bath would use the whole lot.
The reheat time will be longer as the heat exchanger in the hot water cylinder is not perfect. In practice as the return temperature increases the boiler will modulate down and will not achieve 18Kw output, particularly at the end of the reheat cycle when the temperature difference across the heat exchanger is low.
I cannot find any manufacturer documentation to calculate the effect of hot water cylinder heat exchanger efficiency on reheat time. Is it significant in the case of a part L compliant hot water cylinder? Is there any point in paying for a premium cylinder such as the Albion CF80 (other makes exist)? Could I leave the old cylinder (which uses gravity circulation) unchanged except for conversion to fully pumped primary?
Regards,
MJA