Having bought a small generator I'm now reading the manual supplied with it - the manual is not very good.

In the manual is a diagram showing the earthing point (frame) of the generator being connected to a ground spike, but there's no helpful words to advise that this should be done.

Am I supposed to connect the frame of the generator to an earthing spike driven into the ground when in use? What size spike?

This is only a tiddly little generator - 240v/950W rating.

PoP

Reply to
PoP
Loading thread data ...

Reply to
sparky

Order of postings corrected to make sense.

I'm keeping quiet but if the OP searches groups.google.com back in this group and uk.tech.electronic-security, he'll find a couple of lengthy recent threads... Still they boil down to get expert advice from an qualified spark with experience of generator installations.

Reply to
Dave Liquorice

That's why I'm not replying to any more of them. Some people don't understand the differences between the domestic supply and a generator supply system, so they get stuck in this Live and Neutral thing. When you try to tell them the difference, they look at you as though you've got two heads. So now I've given up. :-))

Reply to
BigWallop

Don't worry - I read your earlier comments about live and anti-live ;)

And I fully understood them.....

....but just wondered whether a generator is supposed to have an earth spike :)

PoP

Reply to
PoP

If the generator has safety devices fitted, then most definitely "yes". Otherwise you wouldn't have a safe enough installation.

Reply to
BigWallop

I fully understand where you are coming from and I believe we actually agree, there seems to be a "separated by a common language" problem. B-)

Local Earth - Properly installed connection to the local physical ground via an earth spike etc.

Supply Earth - The "earth" connection provided by the public electricity company.

Generator assumed to have no center tap to the alternator windings or if it does the center tap is *NOT* connected to *ANYTHING*. A generator with a center tap connected to local earth cannot make a safe connection into a normal installation as both generator phases are fixed at half the supply potential away from local earth.

For simplicity I have omited mentioning anything about how any connections are made. Obviously the public supply L and N need to be fully isolated from the CU before the generator phases are connected and vice versa.

I agree that simply to connect the two "phases" from a generator to the L and N terminals of a CU is unsafe. Both generator phases are floating with respect to local earth. It is quite likely that the N line will be at a significant voltage above local earth, if you come in contact with it. Single pole switches will not make the connected equipment "safe" as they only isolate the L connection.

To over come this problem you pick one of the generator phases, doesn't matter which, and bond that with correctly sized cables to local earth, at the generator. This local earth bonded generator phase you connect to the CUs N terminal. The unbonded generator phase to the CUs L terminal. You now have a situation where the N wiring is at, or very close to, local earth potential and all the L wiring is fixed to be at the nominal output voltage of the generator. Single pole switches now work "correctly".

Now the tricky bit. All the circuit protective wiring (aka the "earth" wires in T&E etc) in the building are connected back to the main earth termal next to the CU. The main earth terminal is connected to the supply earth and equipotential bonding is also run from the main earth terminal to the incoming service pipes etc

Trouble is that the supply earth could be at a different potential to the local earth. Depending on the public supply type I think the dangers of connecting the local earth to supply earth change. For TT (local earth spike) and TN-C-S (PME) installations I don't *think* there is much to worry about, as the supply earth is derived at or very close to the premises.

I do have worries about making a local earth/supply earth connection on a TN-S (supply earth provided from supply cable armour or metalic sheath) system. This is the part that one needs to take advice on from a qualified spark with experience of generator instalations.

Finally should the generator chassis be connected to the local earth? Yes.

Reply to
Dave Liquorice

And if the generator has any safety earth leakage device, then placing any of the phase to earth will activate the device and kill the supply from the generator.

That's the situation, yes.

Exactly.

Right. Exactly.

Then the phase you've chosen to stick in the earth will need less than one ohm impedance to be of any in supplying a neutral at the consumer unit and this would need to be calculated correctly in all weather and ground effect situations. It may also trip any safety devices on the generator itself. So that needs further investigation.

Exactly.

But if the supply earth is receiving back fed half phase supply from the generator, which has a phase stuck in the ground at less than one ohm impedance, then the earth, no matter where it is coming from, will have picked up this charge and will supply it back to the connections that already exist.

The two earth potentials must be totally separate. No domestic supply from the grid can be connected to the system if you are going to change over to a generator supply. Any common connection between them will also become part of the supply from both. They must be totally separated in the phase connections and earth potential connections. Totally.

But then you'll supply the earth connections with both local and supply earth potential. Not a great idea in my experience.

At least someone is trying to figure it all out though. :-))

Reply to
BigWallop

All interesting stuff, and thanks for taking the time to point it out.

It would be so, so easy for someone to buy a genny and wire it into the house mains without knowing what the hell they are doing. Thank goodness for a newsgroup like this one I say!

Now if the proposed building regs part P covered genny sales.....

PoP

Reply to
PoP

Hi,

: > > Some people don't understand the differences between the domestic : > > supply and a generator supply system, so they get stuck in this Live : > > and Neutral thing. : >

: > I fully understand where you are coming from and I believe we actually : > agree, there seems to be a "separated by a common language" problem. : > B-) : : And if the generator has any safety earth leakage device, then placing any : of the phase to earth will activate the device and kill the supply from the : generator.

The neutral connection must be made before any earth leakage detection device. Dismemberment of the generator may be necessary to achieve this.

: > Local Earth - Properly installed connection to the local physical : > ground via an earth spike etc. : >

: > Supply Earth - The "earth" connection provided by the public : > electricity company. : : That's the situation, yes. : : > Generator assumed to have no center tap to the alternator windings or : > if it does the center tap is *NOT* connected to *ANYTHING*. A : > generator with a center tap connected to local earth cannot make a : > safe connection into a normal installation as both generator phases : > are fixed at half the supply potential away from local earth. : : Exactly. : : > For simplicity I have omited mentioning anything about how any : > connections are made. Obviously the public supply L and N need to be : > fully isolated from the CU before the generator phases are connected : > and vice versa. : : Right. Exactly. : : > I agree that simply to connect the two "phases" from a generator to : > the L and N terminals of a CU is unsafe. Both generator phases are : > floating with respect to local earth. It is quite likely that the N : > line will be at a significant voltage above local earth, if you : > come in contact with it. Single pole switches will not make the : > connected equipment "safe" as they only isolate the L connection. : : Exactly.

No, it depends entirely on how good your insulation is. Assuming good insulation all round, it means that you become the neutral reference when you touch one of the conductors and you don't feel a thing. This is fine unless there is anything else drawing a current to earth at the same time...

: > To over come this problem you pick one of the generator phases, : > doesn't matter which, and bond that with correctly sized cables to : > local earth, at the generator. This local earth bonded generator phase : > you connect to the CUs N terminal. The unbonded generator phase to the : > CUs L terminal. You now have a situation where the N wiring is at, or : > very close to, local earth potential and all the L wiring is fixed to : > be at the nominal output voltage of the generator. Single pole : > switches now work "correctly". : : Then the phase you've chosen to stick in the earth will need less than one : ohm impedance to be of any in supplying a neutral at the consumer unit and : this would need to be calculated correctly in all weather and ground effect : situations. It may also trip any safety devices on the generator itself. : So that needs further investigation.

Why is such a low earth impedance required? Fault currents will rarely flow through the rod itelf and in the rare cases they do they should be picked up by an RCD. The rod only provides a reference for the whole system. Think of the arrangement as having the very low earth fault loop impedance of a TN-C-S system for faults to bonded equipment (generator permitting!) but the relatively high earth fault loop impedance of a TT system for true faults to ground. This does mean that an RCD on the live and neutral from the generator is essential to catch true earth faults though. I would also be wary of earth fault loop impedance figures when looking at the supply from a small generator - I suspect there will be quite a lot of resistance in the generator and an RCD would be required even if you have the best earth rod in the world.

: > Now the tricky bit. All the circuit protective wiring (aka the "earth" : > wires in T&E etc) in the building are connected back to the main earth : > termal next to the CU. The main earth terminal is connected to the : > supply earth and equipotential bonding is also run from the main earth : > terminal to the incoming service pipes etc : : Exactly. : : > Trouble is that the supply earth could be at a different potential to : > the local earth. Depending on the public supply type I think the : > dangers of connecting the local earth to supply earth change. For TT : > (local earth spike) and TN-C-S (PME) installations I don't *think* : > there is much to worry about, as the supply earth is derived at or : > very close to the premises. : : But if the supply earth is receiving back fed half phase supply from the : generator, which has a phase stuck in the ground at less than one ohm : impedance, then the earth, no matter where it is coming from, will have : picked up this charge and will supply it back to the connections that : already exist.

??? But if it is a true earth then you have the luxury of attempting to charge the whole planet and nobody will care. The problem occurs when you have more than one earth and they are not quite the same. The biggest problem is the effect you may inadvertantly have on your electricity supplier.

For a TT supply, there is no problem whatsoever. TT is convenient in that there is only one possible earth reference, the earth rod. This would provide the earth reference and the installation protective conductors. One side of the generator, all metalwork bonding, etc would be connected to this. The external supply only gives you live and neutral and there is no risk of earth loops.

For a TN-C-S supply, you will have two earths, the supply earth (derived from the supply neutral) and your own earth rod. Your own earth rod is required to provide an earth in the event that the supply cable is cut. I would be tempted to connect the PME earth and the earth rod together but there are two caveats: 1) There is a risk that you might experience more rapid than expected corrosion of your earth rod due to any voltage present on the supply neutral derived earth during normal operating conditions (this shouldn't be an issue since otherwise any cross bonded buried pipework would also suffer) and 2) under fault conditions during generator operation the voltage on your earth rod will rise taking the voltage on the supply neutral conductor with it. This shouldn't be a problem assuming that everything locally is RCD protected, cross bonded and the earth through the rod is reasonable but it may cause some current to flow into the supply neutral and I don't know if the local electricity supplier would be expecting this. I don't know the official answer in this circumstance - it will either be specified in the relevant IEE regs or you will need to consult your electricity supplier.

: > I do have worries about making a local earth/supply earth connection : > on a TN-S (supply earth provided from supply cable armour or metalic : > sheath) system. This is the part that one needs to take advice on from : > a qualified spark with experience of generator instalations.

The same applies to a TN-S system as for a TN-C-S. There is a risk that under fault conditions you will cause an increase in the potential of your bonding which can be seen at the end of your supply cable (on the sheath rather than the neutral in this instance). Again, assuming RCD protection, proper cross bonding and a reasonable earth rod there shouldn't be an issue but I would check with the electricity supplier.

: The two earth potentials must be totally separate. No domestic supply from : the grid can be connected to the system if you are going to change over to a : generator supply. Any common connection between them will also become part : of the supply from both. They must be totally separated in the phase : connections and earth potential connections. Totally.

I don't think that is hugely practicable and in most cases there shouldn't be a problem. In the case of TN-S and TN-C-S supplies I would do a bit of research or consult the supplier to understand what their concerns are with regard to their earth but keeping the earths separate will mean that there are switching devices in the earth, a very bad idea in my opinion. Cross bonding will generally mean that the two earths are effectively connected anyway. If there is any significant voltage difference between the two available earths, then I strongly recommend that you do not use mains applicances outside the house!

Keeping the neutrals and phases separate is obviously a given unless you have some relatively unusual arrangements with your supplier and a whole load of protective equipment to ensure that you don't feed into a dead public supply.

: > Finally, should the generator chassis be connected to the local earth? : > Yes.

: But then you'll supply the earth connections with both local and supply : earth potential. Not a great idea in my experience.

The generator chassis should be connected to earth and the local one makes the most sense since that is the one guaranteed to be present all the time. As I suggested above, connecting the local and supplier earths together is probably the answer anyway.

Have fun,

Dale.

Reply to
Dale Shuttleworth

"Dale Shuttleworth" wrote in message news: snipped-for-privacy@giskard.demon.co.uk...

Correct, obviously.

[Generator winding floating]

This is an IT system - /isole terre/ - floating source and earthed metalwork. It's used in some industrial situations where supply disconnnection in the event of an earth fault would be more dangerous then leaving the power on. It's fine in the sense that a single earth fault won't cause a problem - in fact the fault will go unnoticed until a second one occurs. For that reason IT systems have to employ some form of earth monitoring to draw attention to the fault.

Running your house as an IT system is not permitted, since the indirect contact protection is designed on the assumption that it's a TN system - either TN-S or TN-C-S (PME) - and no earth monitoring is employed.

[BW]

It isn't - although the statement "will need less than one ohm impedance" is pretty meaningless; did he mean impedance to earth, or something else?

Even the earthing resistance at public supply network susbtations only has to be less than 20 ohms for PME networks (although it is typically far less).

Without the RCD it's no different to a non-RCD protected circuit on the TN public supply. This won't catch what you call "true earth faults" either, but such faults shouldn't be possible since all exposed-conductive-parts should be connected to the main earth terminal via their respective CPC's. Anything supplied outside the main equipotential zone should be RCD-fed of course.

I agree. The higher impedance of the generator supply means that the value of Ze (the part of the earth loop impedance exterenal to the house installation) is higher than the value assumed for design, so you can't rely on disconnection time requirements being met, etc. A 100mA time delayed RCD is the best solution here. (If the house installation is TT-earthed then this RCD will (should) already exist and there's no need for another one on the generator.)

[BW]

Quite. Whatever he was getting at, it's so badly expressed that I haven't a clue what he meant, except that he seems obsessed with generator outputs being centre-tapped.

Yes, I agree with all that.

And that. The requirement for an independent means of earthing is in BS

7671 (Reg. 551-04-03).

I don't think that's a problem at all. There are other circumstances in which local earth elecrodes bonded to the PME terminal are recommended.

Again, no problem here that I'm aware of. If your generator to house TN system is properly installed then earth fault currents are contained within your own copper conductors. Anything flowing to earth should either be negligible, or, as you say, quickly interrupted by the RCD. But in any case you do need to consult the supplier - this requirement is in BS 7671, Reg.

551-01-01: "Requirements of the electricity supplier shall be ascertained before a generating set is installed in an installation which is connected to the public supply".

As I've said before, BS 7671 has three pages of requirements relating to generators (which includes UPS's by the way) in section 551. Anyone contemplating a permanent genny installation should purchase and study, and consult their supplier. If in doubt consult a professional electrical engineer.

Here's my attempt at an ASCII wiring diagram:

L o----------------o \ SW1a Mains o----------> L to CU from meter + -------o | SW1: DPCO changeover switch | 100A break before make! N o----------------o | \ SW1b | o----------> N to CU | | +---o | | | | Supplier's E o-----------------------------o Main earth terminal earth | | / | | | | | 16mm^2 | | | earth | ------- | | | | | G.P. | | G.P. = Generator | | | protection, ------- | fuse or CB | | | plus 100mA RCD | | | -- | - | -- | | G( | | | | G( | | | | G( | | | G = generator winding | G( | | | | G( | | | | | | | | Generator | +---.B | | frame -> | | | | B = bonding connection -------.-- | B|\ | | \-------------+ | | | ----- --- Your earth electrode(s) - Re < 200 ohm