I would expect 30mA (i.e. for shock protection rather than infrastructure / fire protection).

However "all RCBO" installs are much more cost viable these days, and even if just using the normal 17th style CU you would normally ensure the power circuits in a given place are on the "other" RCD to the one doing the lights.

Reply to
John Rumm
Loading thread data ...

There's two overlapping requirements covering this.

You need to have a fused connection where cable sizes change, and a circuit has to be fused to protect the smallest cable in the circuit. So, if your whole circuit is fused to protect 1mm cable I would accept a larger cable as a main feed to 1mm spurs. I have done this where I typically have a larger cable running from the consumer unit to a convient breakout point, where 1.5mm cable goes off to individual lighting circuits.

I've used fuse-at-cable-change typically when spuring from a 32A ring to provide a loft light where the lighting circuits are inaccessible or there's a need to have a non-lighting light so you can see when the lighting circuit is switched off. Similarly, I make sure there's an upstairs socket within extension lead reach of downstairs and vice versa.

jgh

Reply to
jgh

But what defines "good quality" for crimps? I've used similar looking crimps to these

formatting link
in the past (with a cycling crimp tool) but they've generally been in (slightly) accessible locations and I've seen debate on the IET forum about whether or not insulated crimps are reliable enough for inaccessible locations.

Reply to
nothanks

When I moved into my present house, the vendors had taken all the fancy brass sockets and switches (it was a while ago) and put back the original 1976 white contract stuff.

But they had managed to snap the 1mm cpc in two of the sockets, which were on a single ring (house less than 100 sq m), and badly connected the live to a third, so that it had no cpc at all and the ring was actually two spurs running from a 30 amp wylex rewireable fuse.

They also fitted a new kitchen and drilled right through the cooker live wire, and then repaired it with a bit of choc block which was hidden behind a fitted cabinet. I noticed the burn mark above the fuse wire carrier, that had actually melted part of the metalwork but it was 13 year before I removed the kitchen cabinet and found the 'repair'.

Reply to
Andrew

Quite - I've seen some real rubbish on sale. Very thin metalwork. Which simply can't grip as hard as thicker.

I only buy from TLC these days. But haven't bought any recently.

My hatred is based on their use in cars. They always give trouble - eventually. And houses tend to have a rather longer life...

Reply to
Dave Plowman (News)

But encounter fewer pot-holes ...

Reply to
Andy Burns

Generally if having made a crimp, you can't pull the wire out then its a good one... the crimp should grip hard enough to deform the wire a little, forming a "gas tight" connection.

Reply to
John Rumm

Are you sure its the crimped bit that causes problems and not the connector bit they attach?

Reply to
dennis

And don't make the mistake of thinking a ratcheting tool is always going to make a good joint as an incorrectly adjusted one just makes a lot of bad joints one after another.

Reply to
dennis

It should. Now do a trial one using some scrap cable and cut off the insulation. It will not be in contact all the way round the conductor, in most cases.

Remember seeing a U-tube where various makes were run up to the full rating of the cable, and even above. Most failed long before the cable. Unlike a double screwed connector.

Reply to
Dave Plowman (News)

Almost always the crimp. Could be worse because it is flex. Replacing with a proper spade etc using the correct crimp tool sorts it. Of course no connector lasts for ever. But a decent one a lot longer.

Reply to
Dave Plowman (News)

I've got a few ratchet tools for those RBY terminals. None is adjustable.

Reply to
Dave Plowman (News)

While true for things like your example of taking a feed to run a light fitting from a 32A socket circuit, its not universally true... For example, an unfused 2.5mm^2 spur from a 4mm^2 radial protected by a B32 MCB.

There is also some nuance in "protect" here. The fusing etc must provide fault protection to the whole circuit, but may not be required to provide overload protection to it all. (a spur from a ring circuit being one example - the 32A MCB will provide fault protection for the single run of 2.5mm^2 cable on the spur, but not overload protection. That job is delegated to the design limitation on the spur of only feeding one single or double socket).

With 6A lighting circuits, the cable sizes are over specified anyway with regards to maximum operating current (for reasons of mechanical durability, and limiting voltage drop).

Reply to
John Rumm

If its the one I am thinking of[1], none of the connectors failed at the full rating of the cable. In fact they all survived well beyond a significant overload - ultimately the cable failed before the connectors

- although that was a moot point since nothing had any insulation left on it at that point (90A though a 2.5mm^2 wire)

[1]

formatting link

Reply to
John Rumm

I'm now more puzzled than before. I could look at the book but its not to hand.

Earlier it was said "No, cable should be the same size throughout the circuit. 1mm is actually adequate for most 6A lighting circuits in houses where the cable length isn't too long."

I thought this wasn't true at the time. Can we confirm that as long as the smallest conductor is still fault and overload protected by a MCB, then all is well?

Reply to
Fredxx

RCBOs are OK for a new installation but probably wouldn't fit on the Wylex board fitted c1992, judging by the space occupied by the MCBs. I'd definitely go for 100mA/30mA RCDs and then RCBOs in a new installation.

Reply to
PeterC

As a general principle you would normally have just one size of cable in a circuit, but there are some exceptions as highlighted.

Which bit?

Yup generally. Fault protection in particular is the one critical, must be done at the origin of the circuit, requirements.

Reply to
John Rumm

If you have a TT installation that is about right (assuming that the

100mA RCD is time delayed if in series with the 30mA RCD).

However it will soon be a requirement for lighting to have 30mA RCD protection on new installations. Although this has pretty much been the case since the 17th edition came out.

Reply to
ARW

That's a pity - I've had an experience of enough of a shock to make me jump back - in darkness (assuming that the lighting RCD tripped) I could have suffered an injury on various edges etc.

I can't recall if my 2 RCDs are in series or not; I suppose if 2x30mA are in parallel, then the lighting should stay on if there's a fault on the ring.

Reply to
PeterC

Which has always seemed a little superfluous in domestic premises with single phase supplies.

Red - Brown Black - Blue

There's no mistaking which is live or neutral in either case.