In the kitchen I have an MK Grid Switch this has a nice neatly labelled switch for each of kitchen fixed appliances.

The Oven (not hob) is a 20A DP switch and is fed from a dedicated 20A radial cct on 4mm2 cable Grid switch feeds to an MK5045 cooker wiring point

Oven is being replaced with a Neff U1ACE2HN0B and information is that it is rated at 5.9kw ..... which to me says 26A

I can't find a Grid switch higher than 20A ..... I know I could increase breaker to 32A ... but would then need higher capacity grid switch

Anybody any suggestions ?

So far only thought is I would need to put a link in bypassing the GRID switch (and fit a blanking plate) and put a DP cooker switch instead of MK5045 connection point. Unless anyone else has a better idea.

If my idea is the option what in neatest way to 'bridge' the 4mm t&e ... use WAGO lever connectors ...

formatting link
are good for 32A or WAGO push connectors rated at 40A
formatting link
Anybody experience of using these ? which is easiest to use ... or is there a better way

Connection will be within confines of the 'back box' so all still protected.

Reply to
rick
Loading thread data ...

The 2nd product code link should have been:

formatting link
Not used either so unsure which is easiest to use.

Reply to
rick

I suppose you could use the existing grid switch to switch a contactor or relay, and have that switch the oven.

For applications like this, the non lever type are quick and easy.

Reply to
John Rumm

apply diversity

NT

Reply to
tabbypurr

How does diversity help with a switch, can you be sure its not going to switch the 26A and weld the contacts?

Its not like heating of cables which is averaged over time its an instantaneous event.

Reply to
dennis

Not only that, for a fixed appliance like an oven, double pole switching capable of proper (i.e. >= 3mm contact gap) isolation would be appropriate.

Reply to
John Rumm

I would be surprised if a 20A DP grid switch did not have 3mm separation.

Reply to
ARW

I was assuming it was SP, but that is possibly an assumption too far.

(still don't fancy a ~6kW load on it though!)