Buderus 800-60 Boiler - Obsolete Gas Valve

Jul 12, 2022 Last reply: 4 years ago 4 Replies

Hi,



I have a Buderus 800-60 boiler (which is somewhat overrated for what it needs to do but that is a different story) and the gas valve is sticking. If the boiler is not used for a week or so then the gas valve needs a little bit of percussive encouragement before it starts working again, more recently that week or so has dropped to a few hours which means that something must be done.



Unfortunately all the plumbing spare sites suggest that the gas valve is now obsolete and no longer available.



Looking at the gas valve, it is a Honeywell VR8615V type which is a generic designation for that particular valve body (specific designation for mine is a VR8615V-1006. The body incorporates a shut off valve and optionally one of a range of modulating valves (fitted in the case of the 800-60). I'm pretty sure that it is the shut off valve that is sticking (although I suppose there is the risk that whatever is causing the shut off to stick will also be gumming up the modulating valve). I'm pretty sure that the solenoid is OK, this is a mechanical issue.



Does anyone refurbish these valves (or know where I can get a replacement)? I suspect a wash through with a degreasing agent might be a solution (assuming that a compatible agent could be found and that the problem is not actually degradation of the valve itself) but I'm not competent to remove the valve and do something like that.



If the consensus is that the boiler has been claimed by obsolescence (it is only 14 years old and absolutely fine otherwise), any suggestions on a replacement? I only need 30kW rather than the 60 the Buderus can deliver.



Cheers,



Dale.


Have you considered dismantling the part?

Having a spare you can dismantle might be an idea?

formatting link
They're not exactly rocket-science.

As it happens I have acquired a (new) VR8615V valve, albeit one without the modulating element which arrived today. Looking at that, and at the valve in the boiler, it appears that whilst the modulating element is attached with a (probably one use) cork (or similar) gasket, the rear cover is made gastight through the use of reusable (although Honeywell probably says they aren't!) rubber gaskets.

It looks like the sticking valve element is a simple rubber dome with a steel cap, which I can replace from the new valve if I have to, having cleaned the seat.

The real challenge might be finding a gas fitter who is happy to refit a valve I have refurbished myself (and prove the whole thing gas tight). I'd have a go but I don't want to add to the ever growing list of exploding houses where people have got it wrong.

It's trivial to check for leaks with a manometer. Spray-leak is good at finding leaks on the valve body.

A fitter is unlikely to install an item you've told him you've dismantled and reassembled. He can test the system up to your gas valve, but not the valve itself.

If you're really worried there are numerous gas detectors on the market.

As I recall the modulating section was a separately available item so I'd be more inclined to simply swap that onto your new valve.