I came home tonight after work to find that my Baxi Solo 3 40 PF is not working.
I switched off at the wall for a few mins and turned the knob on the boiler to off.
Then with CH & HW set to continuous i turned heating on at FCU and turned knob on front of boiler.
Boiler light came on. Fan light came on
But Pilot and Burner light stayed off.
Is there anything I can do before calling a heating engineer.
Thanks
Andy
Didn't find your answer? Ask the community — no account required.
S
Set Square
Depends how competent you are. You should find a diagnostic chart on the back of the removeable panel at the bottom of the boiler. Work through that to see where it leads you. It sounds as if the pressure switch may have failed. This detects that the fan is running, and stops the boiler firing if it isn't. make sure that the pipes and electrical connections going to the pressure switch are ok. But see where the diagnostic chart leads you - it will tell you how to interpret the little LED indicator lights.
R
raden
In message , Andy Pandy writes
Probably faulty air pressure switch or knacked pcb.
Is the ignition neon coming on, can you hear the spark (a ticking at about one second intervals)
If so, then either the pcb or pilot valve
A
Andy Pandy
Thanks Guys
When I got up this morning the electricity was off.
I reset the trip and it went straight off again.
I turned FCU to boiler off and elecricity stays on.
It seems the problem got worsr over night!
At least yesyerday I could get 2 lights on and no electricity trip.
Geoff
I can hear nothing (could not yesterday before triping started anyway)
Set Square
Thanks I have took the cover off an will look at diagram. I also downloaded a nice pdf file for Baxi maintenance just now so will look at that.
A
Andy Pandy
Wow it gets better
I have taken the front cover off and have removed contol panel and have eased the PCB out.
Every time i have been turning power on at FCU then the power has tripped in the house. (only since this morning)
I have checked on price PCB ( one or two places, new and reconditioned)
I have checked all wires and pipes to the pressure switch.
My situation is now this. i do not know for sure that it is the PCB so have tried one or two things to eliminate the fcu , clock, etc (easy stuff but none the less).
I now arrive at this.
I have taken the plug connector out of the PCB that takes a live , neutral and earth to the pump (so totaly isolating pump) and now when I put FCU on at switch, the electricity does not trip at the consumer unit. When I then turn the control knob the same lights as before come on ie Boiler light and Fan light (though as i stand on a chair and look at the fan it is not turning!)
So im back to my original position as my first post only yesterday i was at this position without the need to isolate the pump to maintain electricity to the house.
Is this indicative of a pump problem that got worse over night ?
Is ther a test for the pump that I may do (maybe plug into socket on ring (L,N,E and see if consumer trips or pump works?)
is there a way to test the PCB without actually buying another one.
Realy appreciate sugestions
thanks Andy
A
Andy Pandy
Hi Guys
Sorry to be a pain but I must post this.
I was concrned as i read my last post
Fan not running but light on!
So i turned boiler aon and as the Fan On Light illuminated I saw the fan turn a smidge but was obviously struggling. i turned all power off and manually turned the fan,, it is really stiff and screeches.
Wow it seems that this is the problem but why is the connection of the pump now tripping the house electricity?
Shall i take it out and wd40 or greese or should I replace?
In my first post I thought that the fan was on simply because the light said so ,, but now as I have took cover off i can see the fan not turning.
Andy
J
John
There is if you have a length of 3 core flex and a plug with 3 amp fuse. It would be better to test the insulation with a megger but if you haven't got one
If the pump is your problem you might not need to
>
S
Set Square
Sounds like the 'fan on' light simply means that power is being supplied to the fan. There is probably another light which comes on when the pressure switch switches - indicating that the fan is *really* running.
I've not had too much success reviving stuck fans - leave it to the experts like Geoff, and get one of his re-conditioned units.
To answer the question in your previous post, you can test the pump by putting a 13A plug on its cable (with a 3A fuse in!) and plugging it into the ring main. If it's ok, have a close look at the connections in the boiler - you might just have disturbed something and caused a short in the pump department.
R
raden
In message , Andy Pandy writes
Yes, I misread that last night as fan running
... new one on it's way !
A
Andy Pandy
Thank you all
Watch this space!
Next episode tomorrow night.
Andy
A
Andy Pandy
Well
New Fan installed and boiler fires up fine. Brilliant.
Only prob now is that when I connect the pump to the PCB the Consumer unit trips still !
Could the fan becoming stiff (in the first instance a couple of days ago) and so not working have somehow put load on the pump or PCB as it was struggling to rotate.
I will test Pump tomorrow with a flex to socket on the ring!!
Fan is excellent Geoff thanks, but stay by the phone.
Andy
R
raden
In message , Andy Pandy writes
Water in the pump electrics ? Take the cover off and have a look
No, they're both powered directly via relays on the pcb
And I bet it'll trip it out
A
Andy Pandy
No water found
Yes it did as soon as I connected to the ring.
I fitted a new pump today and all (fingers crossed) seems fine.
Thanks Geoff
Old fan will be send on Monday.
Andy
R
raden
In message , Andy Pandy writes
Not easily, I have a test rig which simulates the inputs and outputs.
You need to simulate the temp sensor, the APS, etc and have some means of simulating the flame sensing. Just not worth it for £30, delivery and VAT
J
John
You would be better testing the disconnected pump with a Megger. Pumps are notorious for suffering leakage into the terminal box or even worse into the windings. Worth keeping in mind that its often possible to change just the "top" of the pump without removing the volute casing. IIRC there is a "universal" replacement pump top produced by Ideal