Baxi control board

Nov 09, 2016 6 Replies

Baxi Barcelona, which has been upgraded to 100He spec



On the original control board there were 2 jumpers .. Both were removed as this boiler is connected to a thermal store



J1 to set to 100,000Btu/h J2 to turn off modulation



New board has 4 jumpers J1 Red J2 Blue J3 Blue J4 Yellow



Am I correct that J1 & J2 are the same .. and therefore should be removed ... and removing J3 should also be done to prevent limiting of output temperature



J4 remains as this is a standard short flue



...REMOVING< Jumper 1 limits the output to 52,000 btu's Jumper 2 Increases the output to 100'000btu's Jumper 3 limits the flow temp from 82°C to 63°C - optimum condensing temp,thermal stores Jumper 4 provides low gas rate ignition sequence, for long horizontal and vertical flues

so 2 and 3 out in your case If you are still having explosive ignition problems remove J4 Phone Baxi for confirmation

-
1000,000 Btu/h and when used with a Thermal store. Also read elsewhere that if you remove 1 & 2 .. its sets to 100.000Btu/h and turns off modulation

Are you sure that I should have jumper 1 in place ?

Looks like Explosive ignition issue may now be resolved (earth wire harness issue) so left 4 in

I found a later manual on-line:

formatting link

page 22: If the installation requires a greater output to achieve the desired room temperature, this can be increased to 31.18 kW (103,000 Btu/hr) and the boiler can be adjusted as follows: a) Draw the control PCB forwards out.. b) Remove all three jumpers.

If the boiler is to be used in conjunction with a Thermal Store, the boiler can be adjusted as follows: a) Draw the control PCB forwards out .. b) Remove jumper 2

Just seems a bit odd ... remove 1,2 & 3 for 100,000Btu/h But remove only J2 for thermal store

also found this on-line ... has even different recommendation:

formatting link

post#5 advises set jumpers to: 1 in, 2 out, 3 in for Thermal stores

So far convinced 2 to and 4 in are correct, still unsure about 1 & 3

Finally found the official answer - got a Tech note from Baxi, may be of use for others:

System up to 75,000 Btu/Hr Ji in J2 in J3 in

System up to 100,000 Btu/Hr J1 out J2 out J3 out

Thermal Store compatibility J1 in J2 out J3 in

J4 in for normal flue, out for long flue, and slow rate ignition

I admit i don?t know much about thermal stores but would have thought that it would be better to limit the flow temp to

63°C for optimum condensing temp i.e J3 Out

-

Trying to get 'best advice' not easy ... but the above at least is how jumpers work. The store is set to 60C currently can't be set higher due to Underfloor Heating - I may fit a blending valve to allow store temp increase but limit loop to 50C

NuHeat advised setting temp on flow to 75C to ensure fast enough recovery time on HW in tank when fro exampling running a bath.