Can I legally wire a sub panel from the main breaker of my main panel?
I was planing on having a 200A main service-rated panel in the basement then a 200A non-service-rated panel (i.e. sub-panel or lug panel, without a main breaker) upstairs. I think this will give me a lot of flexiblity as to which branch breakers I put where. The connection for the sub panel would start on the load side of the 200A main breaker of course, if this is even legal.
Also, lets just assume that I've met the requirement allowing me to use my main breaker inside as my means of disconnect and overcurrent device.
(PS. This is all new contruction.)
--wahzoo
Didn't find your answer? Ask the community — no account required.
Gee whiz info. A branch circuit is the wiring from the last over current device...
M
Mark or Sue
Technically, I believe this is legal. But implementing may be challenging. First question is does your main panel have feed through lugs? If not, you need some way to tap into the bus to continue that 200 amps. Some panels have "sub feed kits", and you'd have to find one rated for 200A. Some panels also have a limitation on the maximum breaker stab current which is less than the total panel rating. So make sure you find a panel with each stab rated to 200A, or it has a feed through lug at the bottom. You'll also need to deal with wire bending space requirements, but these should be OK assuming you find a sub feed lug or feed-through designed for that panel.
You will have to install a 4-wire feeder to the subpanel using 2/0 copper or 4/0 aluminum. The 4th grounding wire must be at least #6 copper. Also make sure you have enough big holes in your neutral bar.
-- Mark Kent, WA
M
m Ransley
you are overloading
C
CLSSM00X7
Hi,
You can do it that way but it isn't code. It is safe becasue the main breaker will shut down if you exceed its rating. Check the rating for the main panel. The total amp rating. I am guessing it isn't over 250 amps. Why do you need 200 amps for a basement? that is 10, 20 amp circuits.
candice
A
AJScott
Speaking of overloading, shouldn't your head be exploding or something within the next 5 minutes or so?
Sorry, but some unseen force drove me to ask. It was completely against my will.
AJS
E
Eric Tonks
200 amps is a lot more than 10 20amp circuits. It could be 40 or 50 circuits. You don't load each circuit to the max. 200 amps still sounds a lot unless he is welding or running industrial equipment.
Z
zxcvbob
How about a 100A or 125A main lug panel upstairs, fed from a 2-pole 100A breaker in the service panel in the basement? That would give you plenty of room for expansion, and you could run a lot smaller and easier-to-handle wire to the subpanel -- #4-3/wg, I think, although if the distance is very far you might want to run two #3 hots and #4 neutral and ground. Are you gonna use a conduit to connect the 2 panels, or run a big cable?
Best regards, Bob
M
Mark or Sue
Overload is determined by the Service calculation and not the number of circuits installed. The main panel is rated at 200 amps if the breaker is rated at 200 amps, and that is all he'll get regardless how it is apportioned between panels. Using 100A feeders is a more common approach, but these can be problematic if you have some large items on those feeders like an electric range, clothes dryer, and airconditioning compressor -- doesn't leave much ampacity left. Usually, you leave the big stuff in the main panel and run the general lighting and small appliance circuits form a subpanels if necessary. But if you're trying to keep everything on a single floor in a given panel, this is where it gets tough.
A dual 200A installation will solve a lot of capacity problems, but I don't know why panels are desired on different floors. A single 42 slot panel is usually the least expensive installation. But if more than 42 circuit breakers are needed, then its gets more costly and complicated.
-- Mark Kent, WA
J
John Hines
There is a limit, I believe it is 6 items, that have to be turned off to shut off power.
To put it another way, unless the two panels are right next to each other, if you have more than 6 circuits in the subpanel, it needs it's own single shut off (service disconnect).
In this case, I don't know if you can get away without feeding the sub from a breaker in the main panel.
E
EL
If you don't feed the subpanel through a breaker smaller than the 200 amp main the connection between the entrance panel and the subpanel will have to be made with at least 2/0 copper.
I run 6 subpanels in my home, each fed through 50 or 60 amp breakers in the entrance panel that in turn are fed from one 200 amp breaker. The connections to the subpanels are are made with #6 copper.
Boden
John H> snipped-for-privacy@hotmail.com (wahzoo) wrote:
M
Mark or Sue
You're confusing service panels and subpanels. The 6 switch rule is for service disconnects. A sub panel is by definition fed from a breaker in a panel, so turning off that panel shuts off all of its sub panels..
A subpanel does not require a main breaker if it is protected by a breaker in its feeder. An exception to this rule would be subpanels located in a detached structure -- the structure must also have no more than 6 throws of the hand to shut it down and those disconnects must be located at the structure.
He has no choice but to make the panel a subpanel, which means feeding it from a breaker. If a service rated panel was attempted, he'd violate the requirement that the disconnects have to be grouped, and probably violate the length limitations on how far service conductors can enter a structure.
-- Mark Kent, WA
A
Art Todesco
service disconnects. A sub
panel shuts off all of its
its feeder. An
the structure must also
must be located at the
a breaker. If a
disconnects have to be
conductors can enter a
W
wahzoo
I don't get why if a main breaker shuts down it isn't safe. I would think it would be just the other way around: If a main breaker fails to shut down it isn't safe.
Check the rating for the main panel.
In my original post I said I'll have a 200 amp panel. Are you saying there's some other rating, the "total amp rating" could be other than
200 amps?
Why do you need 200
Do you really think I meant that I'll have 200amps of equipment in my basement? The idea was to have two 200 amp panels, one in the basement one on the top floor. Branch circuits would run out from the basement panel to circuits in the basement and 1st floor. The top floor panel would handle the rest of the house. Of course, it would be up to me to make sure the sum of the amps of the branch breakers in both panels did not exceed 200 amps. I like this flexibility.
W
wahzoo
circuits installed. The main
all he'll get regardless
approach, but these can be
range, clothes dryer, and
leave the big stuff in
a subpanels if
given panel, this is where
know why panels are
expensive installation. But
The house is three floors plus a basement. I just thought by having multiple panels I could save wiring home runs all the way down to the basement. (The main panel is in the basement for security reasons.) Also having 2 200amp panels would allow future flexibility with adding or moving circuits. The thing I forgot to consider is how big that feeder between panels has to be, as you pointed out. Thanks. Maybe it'd be be better to have have 2 100amp sub panels fed from the main
200amp service panel.
W
wahzoo
Right that would be better. Or I just might have two 100amp sub panels. Yes I'm using IMT --embedded in concrete block for the risers, surface attached for all other wiring. This is for a completely concrete house, floors too, except for a few internal partitions.
W
wahzoo
Amen, but really, 6 subpanels! Pray tell what's the advantage you're getting with that?
J
John Hines
Same as you, shorter local runs? Concentration of activities, like all kitchen breakers in the same panel?
J
John Hines
disconnects. A sub
shuts off all of its
Ok, I'm not the first person to be confused by the NEC.
IMHO, if you have more than 6-8 circuits in a sub-panel, it should have a single breaker, in it, which shuts down that whole sub-panel.
Feeding a sub-panel from a breaker, gives the ability to completely kill that sub-panel, making it much easier and safer to work in.
M
Mark or Sue
service disconnects. A sub
panel shuts off all of its
All subpanels are protected by a breaker, it just isn't in that panel it is in the parent panel.
You get that capability in the parent panel breaker feeding the subpanel. There is no rule preventing you from having a breaker at each end, but you have to buy two large breaker this way instead of only one. In a setting where you can't control access to the parent panel (no lock out tag out or people/kids ignore signs) then maybe you'd want a main breaker in that subpanel.
-- Mark Kent, WA
M
Mark or Sue
Depends on a few factors (you aren't NEC guru Joe Todesco's brother are you, trying to see if I step bady in the code?).
First, I'm assuming that the 100A main breaker will remove power to both panels
-- is this true? The conductors to the subpanel are not required to be larger than the conductors to the main service. These would normally be #4 copper or #2 aluminum for 100A service. If your service is larger than
100A, then you could use #3 copper if rated for 75C (such as SER cable and THHN individual conductors) or #2 copper if using NM or UF cable. You also need 4 wires, as the grounding wire and neutral wire must be kept separate in the panel and the neutral bus isolated from the chassis. The
4th grounding wire only needs to be #8 copper.
If power in this panel is NOT removed when the 100A main is turned off, then you can have a 3-wire connection to that other panel, but these are unfused service conductors. The connections would have to be made per service conductor rules (usually conduit w/special bonding rules), and you really need to do a load calculation to make sure you're not overloading the service. The neutral bus stays bonded to the chassis in this case.
Panels and services are always sized by calculation and not by adding up breaker handle ratings. Breaker handle sums typically exceed the rating of each service leg (i.e. leg 1 breakers would exceed 100A and leg 2 breakers would exceed 100A). But the service calculation can not exceed 100A or else you need to upgrade it. The breaker that feeds a panel must be large enough to carry the calculated current, and the wires installed must be rated for the load. If you install a larger breaker for future expansion, then the wires must be sized according to the main breaker protecting them.
Touched a lot of options here, did I answer your question???
-- Mark Kent, WA
A
Art Todesco
trying to see if I step
Don't know Joe Todesco. Just a retired EE working mostly in electronic design, however, I have been known to look at NEC ..... but not in a bunch of years.
panels -- is this true? Yes. The
to the main service.
service is larger than
THHN individual
the grounding wire and
from the chassis. The
Even if the original panel had a "combined" neutral and safety grounds?
you can have a 3-wire
connections would have
rules), and you really
The neutral bus stays
breaker handle ratings.
1 breakers would
can not exceed 100A
enough to carry the
install a larger
main breaker protecting
So, the conductors can be smaller than #4 CU or #2 AL if the calculated maximum current is less than 100 amps? How do you calculate the current on an outlet string with a 20 amp breaker?
Thanks for the info.
Join the Discussion
Have something to add? Share your thoughts — no account required.
Didn't find your answer?
Ask the community — no account required
Report Content
You are reporting this content to the moderators. They will look at it
ASAP.