You might want to recheck that math. At the ratio of 1 sq ft for every 150 sq ft of attic floor, you need 16.7 sq ft, not
- That is 2400 sq in. With a 2" wide vent, you'd need
But there is another thing missing here. That ratio of
1 sq ft of venting for every 150ft of attic floor is for TOTAL venting, which is supposed to be divided between intake and exit. So, for the example, you'd need only 50 ft of soffit venting. Using soffit venting on both halves of the roof, you'd have twice that. I was making this mistake earlier today when I was doing the math too.And the minimum acceptable venting ratio is 1 sq ft for
300 sq ft of attic floor, so I should have plenty.
If anything, you probably need more with big fans. One big issue with attic fans, and why most experts are against them is that they create negative pressure in the house. This winds up sucking air conditioned air through any available route, eg ceiling recessed lights, up into the attic. So, you're increasing the cooling load on the house.