Main breaker location

Jul 04, 2009 24 Replies

Thanks for a helpful response.

I looked up the appraisal and found it was built in 1965.

I think the important thing is that the circuits are protected.

In the box there are 4 breakers(among others) next to each other with a bar attached to all of them with the number 40 on it. I tried to see where the wires led to, but there were too many wires in the box.

Another interesting thing is the ground wire for the box.

Instead of an insulated wire going to the copper ground rod, it APPEARS that the uninsulated ground wire goes behind the brick and comes out a hole close to the grounding rod.

There is also an uninsulated wire going from the grounding rod to the outside AC unit. I am not sure that is up to snuff. :-)

Take care, Andy

FWIW, grounding electrode conductors can be either insulated or bare. Even houses built in 1965 were required to have service disconnects. I suspect that you may not be understanding the wiring in the panel you have, and that it may very well be a split buss type. A picture would clarify your situation

...

Using the picture at this site, I determined that the panel is NOT a split bus.

formatting link

When I do repair work, I don't make assumptions.

If you cut corners on plumbing you may have a leak. Mistakes in electrical work can be deadly.

Andy

Using the picture at this site, I determined that the panel is NOT a split bus.

formatting link

When I do repair work, I don't make assumptions.

If you cut corners on plumbing you may have a leak. Mistakes in electrical work can be deadly.

Andy

Split buss panels will look different for each manufacturer. Sometimes the internal set of wires from one of the mains to the bottom section is pretty well hidden. Certainly an easy enough thing to figure out, by killing each double pole breaker and seeing if any single pole breakers go dead simultaneously

.

om...

:

Killed the double pole breaker and none of the other breakers went dead.

I will try to anticipate your next question.

No, I will not send you the box because you don't believe it's not a split bus panel. :-)

Andy

Killed the double pole breaker and none of the other breakers went dead.

If it were a split buss panel, you would undoubtedly have more than a single double pole breaker

It is entirely possible that the service was installed improperly, especially if the meter equipment and panel are of a mid 60's vintage

I will try to anticipate your next question.

No, I will not send you the box because you don't believe it's not a split bus panel. :-)

Andy