Interconnected smoke detectors - no circuit breaker?

Home built in 2005. These are interconnected Fireex smoke detectors (I believe because they have a yellow wire connected to the red wire). All the breakers are marked, but I don't see one for the smoke alarms.
Now I was away on business and my wife had an alarm chirping and couldn't get it to stop so she literally in wired it while it was hot! Could have killed herself.
Problem is I want to rewire it and I don't know how to cut the power to it since there is no breaker.
Thoughts?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

There HAS to be a breaker. It will likely be shared with another circuit - in USA the code required the smoke detectors to be on AFCI breakers, I believe.they are GENERALLY connected to a bedroom circuit - which also requires AFCI protection.. This is NOT a code requirement but is acceptable best practice..
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Saturday, March 25, 2017 at 4:04:07 PM UTC-4, snipped-for-privacy@snyder.on.ca wrote:

Agree. And it obviously can't be hard to figure out which breaker it is.
- in USA the code required the smoke detectors to be on AFCI

I don't believe that is correct, either then or now. AFCIs were required for circuits in bedrooms, what year that went into effect, IDK. But smoke detectors are not necessarily required to be in the actual bedroom. Here I believe having them close to the bedroom is sufficient. If the smoke detector is in a hallway right outside a bedroom in an area not required to be AFCI protected, then I don't think it has to be.
I believe.they are GENERALLY connected to a bedroom circuit

I don't see why connecting smoke detectors to a bedroom circuit is best practice.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
The smoke detectors are most likely connected to a breaker that won't normally be turned off by a homeowner. Typically it is wired to the furnace circuit. Open up the panel, it should be the only breaker with 2 hot wires connected to the breaker.
Note: items like furnaces have service switches at the unit to prevent anyone from powering up the device without the service personnel knowing about it. This is true for remote AC units as well.
Dan
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Saturday, March 25, 2017 at 4:28:50 PM UTC-4, snipped-for-privacy@yahoo.com wrote:

Maybe, assuming the breaker is rated for double tapping. I've seen quite a few homes here in NJ with hardwired smoke detectors both old and new construction, none had double tapped breakers on anything.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 25 Mar 2017 13:23:20 -0700 (PDT), trader_4

For the last few cycles AFCIs have been everywhere. Even in 02 when they first showed up in bedrooms the smokes had to be on the AFCI.
I bet the smokes are on a breaker with one of the bedroom ceiling lights,
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 25 Mar 2017 20:26:29 -0400, snipped-for-privacy@aol.com wrote:

They have to be on an AFCI, but it does NOT have to be on a bedroom circuit. THAT is what is "best practice" and not required by code.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Saturday, March 25, 2017 at 8:55:53 PM UTC-4, snipped-for-privacy@snyder.on.ca wrote:

Please cite for us the code section that requires AFCI to be on an AFCI. For starters, it makes no sense. As I said, it's my understanding that the requirement for AFCI is tied to where the outlet is, not to what's on it. Today because AFCI is required in the living spaces, if the smoke detector is in a hallway, it would need to be on an AFCI. But the poster's home was built in 2005 when AFCI was only required in BEDROOMS. If his smoke detector is in a hallway, AFAIK, there was no requirement that it be on an AFCI. His house could be prefectly code compliant with the NEC code when built and if so, it's still code compliant today. If you have a cite for the code section that says that smoke detectors here in the USA must have been on an aFCI in 2005 or even today, I'd like to see it.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 26 Mar 2017 07:40:48 -0700 (PDT), trader_4
I assume you mean "that requires smoke detectors to be on an AFCI"
210.12 Arc-Fault Circuit-Interrupter Protection. Arc fault circuit-interrupter protection shall be provided as required in 210.12(A) (B), and (e). The arc-fault circuit interrupter shall be installed in a readily accessible location. (A) Dwelling Units. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas shall be protected by any of the means described in 21 0.I2(A)(l) through (6)...
... and goes on to list all of the acceptable types of AFCI That is pretty unambiguous. Bear in mind an "outlet" is "A point on the wiring system at which current is taken to supply utilization equipment" (Article 100)
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sunday, March 26, 2017 at 11:03:02 AM UTC-4, snipped-for-privacy@aol.com wrote:

Which again is exactly what I said. That the code doesn't specifically say that smoke detectors must be on an AFCI, only that the outlets in certain locations must be and that it's when a smoke detector is in one of those areas that it becomes covered, just like a receptacle would. What you cite is current code, which again, I said results in smoke detectors being on AFCI by virtue of where they are located because now bedrooms and hallways are required to have AFCI.
BUT, the poster's home was built in 2005. And I believe back then, AFCI was not required in hallways, only in bedrooms. So, I believe his home could have smoke detectors in hallways outside a bedroom on a non-AFCI circuit and it could have been code compliant then and it's still grandfathered today.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 26 Mar 2017 07:40:48 -0700 (PDT), trader_4
There was a requirement for smokes in every "sleeping space"
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sunday, March 26, 2017 at 11:04:28 AM UTC-4, snipped-for-privacy@aol.com wrote:

But depending on where he's located, there may not have been a requirement that the SMOKE DETECTOR also be in the bedroom. If the smoke detector was in the hallway outside the bedroom, which was and still is permitted in many locations, then AFCI was not required in 2005. And if it was not required in 2005, then there is no need to update it now. Do you agree?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sunday, March 26, 2017 at 11:44:49 AM UTC-4, trader_4 wrote:

On the other hand, if they're all interconnected and on the same breaker, a nd even one is in a bedroom, then the AFCI is probably required.
I'm not sure that's a good idea, really. If you have an arc somewhere and it trips the breaker, hope it kills the circuit before starting a fire. An d there's no other source of ignition (smoking, unattended cooking, etc.) t hat burns the house down while the smoke detectors are inactive.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

That is why they require battery backup.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Monday, March 27, 2017 at 9:38:24 AM UTC-4, snipped-for-privacy@aol.com wrote:

, and even one is in a bedroom, then the AFCI is probably required.

nd it trips the breaker, hope it kills the circuit before starting a fire. And there's no other source of ignition (smoking, unattended cooking, etc. ) that burns the house down while the smoke detectors are inactive.

I think you'll find whether a hardwired smoke detector needs to have battery backup or not varies from state to state. IMO, it's overkill and a nuisance. A friend here has a new home and it has about 10 of them that start beeping for a new battery within a year. Why that is, IDK. You would think the battery is only there for backup and hence would last close to the shelf life, but they don't.
Every fire death I can recall in the news, it was not the result of AC power being lost to alarms that were working. The typical scenario is no smoke alarms, smoke alarms removed, smoke alarm broken, smoke alarm with a dead battery, etc. My house has AC only alarms and that's what I prefer.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Monday, March 27, 2017 at 8:08:53 AM UTC-4, TimR wrote:

Yes, I think we all agree AFCI would be required for new construction and back to whenever the code requiring them went into effect.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 27 Mar 2017 08:18:26 -0700 (PDT), trader_4

The problem is if you have a permit for anything related to a sleeping space, you will be coming up to that code. You are actually dealing with multiple codes too. You have the life safety portion of the building code (NFPA 72/NFPA 101) and the electric code. These days most states are using a model code like the ICC to write theirs (driven by insurance companies) so things like smoke detector placement and requirements tend to be the same across the country. If your insurance company is not looking, older homes may not comply to any of this but those people are becoming more intrusive, particularly if you are changing companies.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

No; in fact, they should *not* be in the bedroom unless there is an expected source of ignition in the bedroom (e.g. an idiot who habitually smokes in bed).
Smoke detectors should always be *outside* the bedrooms: if a fire arises elsewhere in the house, by the time a detector *inside* the bedroom alerts to the smoke, at best, precious time has been lost -- and at worst, the sleepers are already dead of smoke inhalation.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 27 Mar 2017 23:58:54 -0000 (UTC), Doug Miller

That is why they are supposed to be interconnected. If you are really doing this right, the smoke going off anywhere will set off all of the bedroom smokes. Prior to the interconnection rule, the smoke was required to be in the hall outside the sleeping rooms ... and it still is. Now you need a smoke in each sleeping room, one outside the sleeping rooms and at least one on every other floor. This will be triggered if a permit is pulled for any other renovation and the only exceptions are if you can't do it any other way but opening up drywall you were not going to be in anyway. This is defined in ICC building code R.314 which is derived from NFPA 72. These codes tend to be adopted by states as their own.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Monday, March 27, 2017 at 8:30:32 PM UTC-4, snipped-for-privacy@aol.com wrote:

That's what they do with new construction here. Which solves the problem Doug is talking about, ie whether one inside the bedroom or one just outside, may miss early detection. Given how many fires start from smoking in bed, requiring one inside the bedroom seems like a very good idea to me. And like you say, the interconnection is a big plus, a fire starting in the basement you'd get alerted long before smoke reaches a second floor bedroom.
Still, from casual observation of the news, it seems that probably 95%+ of the protection comes from just having a working, unconnected alarm near or inside a bedroom. All the fatal fires I can recall reading about, there were either no smoke detectors, broken ones, disconnected ones, dead batteries, etc. But getting an early warning from interconnected alarms, multiple alarms, etc can also lessen the fire damage or avoid an actual fire, by getting to whatever is going on before it's too late.
Add pictures here