Scenario:

Have an inground pool. Have a well with a submersible pump. Both are wired to two 20amp breakers so that they can be turned off close to the pool - underground wiring.

All was fine until ~ 1 month ago. Now, when the circuit for the well pump is turn ON, and you take a dip in the pool, you will get a electrical tingling sensation. Turn the breaker OFF and there is no charge.

Could there be a break in the insulation of the underground romex between the pump and the breaker which caused the entire ground to "charge" and therefore "charge" the pool water?

It's OK as long as the breaker is tuned off - but to me, it looks like I will be digging an 18" trnech the 20 feet or so to the well with a new line.

Reply to
Steve

Thanks - I was just looking for confirmation of my suspicions.

The new breakers are actually GFCI - the romex to the pool is a new run as is the power from the house panel. The line to the well pump probably shoudl have been replaced when we did the pool - hindsight.

The previous homeowners was an idiot - they put the pool in and ran the power to the pump 1/2 inch undergraound along a sidewalk and patched it into teh 20 amp service breaker for the downstairs heatpump - just plugged it in.

I had the whole thing re-routed (I don't mess with electricity) and done properly. Just missed replacing the run out to the well pump.

Reply to
Steve

I would call an electrician before you end up as "Steve Soup"......

Reply to
Dr. Hardcrab

When you turn the GFCI breaker off you don't feel the tingle? Then it cannot be leaking current to ground, or the GFCI would trip. (You do test your GFCIs don't you...)

Even before you said that I questioned your story. Lets say there is a nick in the insulation. Why would current flow through the ground, through the pool, through you, and then back into the ground; when simply going to ground (avoiding the pool and you) is so much more direct? "Charging the entire ground" would trip the breaker, even if the GFCI was defective. I don't know what your problem is (and you should have called an electrician long ago!) but it is not a nick in the well pump circuit, unless that wire goes through the pool.

Reply to
Toller

Steve posted for all of us... I don't top post - see either inline or at bottom.

I would not nessarily blame the wiring itself. The pump itself could be shorted. Please post what the resolution was...

Reply to
Tekkie®

it would take a massive ground fault to electrify the whole pool. A large groumnd fault should trip a GFI.

Something is strange.

But if you feel a shock int he water, it is VERY DANGEROUS.

Get someoine who knows what they are doing to look at it.

Mark

Reply to
Mark

Well, I guess we would never find out if they guy that got killed felt just "a litle tingling" or not, cuz he's dead.

Here's an easy one; supply line. He said that both GFCI breakers were near the pool. If the previous owner is as stupid as it seems, the incoming line that supplies power to the two breakers is probably not GFCI at the main panel. A nick in this line would energize the pool if it were close enough, or if the soil types were such that the path through ground water or pipes to the pool then to ground was best.

-Kevin

Reply to
kevin

is it really all that dangerous? A little tingling never killed nobody. Plus you are surrounded by water which the electricity will happily pass through just as fast as your body. of course if you happen to swin up to and touch the source of the leak, then you will have a problem.

I'm actually having a hard time thinking of a scenario that would significantly energize the pool without triping the GFCI or the breaker.

I suppose we should ask if the pool is actually grounded?

Reply to
CL (dnoyeB) Gilbert

As the OP is already sure the previous owners were nuts.

Don't discount anything.

First,.... GFI breaker or outlets should NEVER be used with motors. (well pumps and swimming pool filters both use them) They don't work well. The starting currents in motors can fry the electronics in a GFI

And a GFI should NEVER be used to fix a "no ground" problem.

And NO gfi is foolproof, they can go bad, and often do and the test button won't always show a problem

I've seen the same idiots who fixed fuses that kept blowing by shoving pennies in. Move into breakers and fill the handles with crazy glue to keep them from tripping.

Make sure all the motors & pump bodies are properly grounded. swap breakers with known good units.

And don't forget to check any "pool lights" as well

And don't swim in the pool if it tingles, or at least leave a note for your next of kin to let us know what the final outcome was.

AMUN

Reply to
Amun

If the startup current from a motor fried a GFCI, then the human who installed that GFCI was defective. In Europe, some GFCIs are installed for everything in the building - not just selected circuits. Why then do those GFCIs not fry. Furthermore, if a motor trips a GFCI on startup, then the motor has an internal defect; leakage currents that are too high and that get worse when the motor is started.

At first glance (based only upon limited information currently posted), the pool has two major failures. First is massive leakage from the pump into the pool. Second, GFCIs are not working properly either due to erroneous installation or due to internal failure. Both primary and second protection systems have failed.

Bean counter type management convinced themselves that a little leaking around O'rings also was not a problem. After all, the proof was in Space Shuttles that did not explode. However people who deal in reality knew that O'ring leakage was a problem so serious that space shuttle flights should have been terminated.

We are suppose to learn basic concepts of life from the news. However someone even here posted:

This could only be posted by one who never learned even basic lessons of life from the murder of seven Challenger astronauts. This is a post typical of someone whose intent in life is to kill others.

The levees did not break during Betsy and Camile. Therefore the levees would not break with Katrina. At what point do we look to humans and say, "There lies the real source of all problems". A president told us that no one expected the levees to be breached. At what point do we recognize problems are due to human failure - from things such as denial.

Same applied to electric tingling in the pool. It is considered a precursor to human death. Get it fix yesterday. If this post is too complex, then read Amun's response as quoted below. Don't be in denial like some presidents and Thiokol managers that we know. Learn, if from no where else, from why people were killed. Denial is akin to criminally negligent homicide - or why accidents are routinely and directly traceable to human failure. Described are symptoms of a failure of both the primary and backup protection systems. Tingling in a pool is that dangerous that every poster here should have said so.

Meanwhile, I have serious reservations about how the pool was safety grounded. Grounding may be so in violation of code as to require (worse case) pool removal. Based upon how the pool was electrically connected, then a serious evaluation of pool safety grounding is immediately necessary - and maybe an investigation so that charges be filed against the person who installed electrical wiring. The symptoms as described here are that serious.

No > As the OP is already sure the previous owners were nuts.