Electrical Questions

My electrician just installed some standard 3 prong switches and outlets. I noticed he stuck the wires in the back rather than screw them on the side. Is this acceptable practice and usually code? I was worried they may come loose, especially as I went around pulling them out of the box to see the work performed.

Additionally, we notice that every time our 4 tone AC unit starts, all the lights in the house dim for a couple of seconds. Is this a sign of danger, and what should I check to be sure our service is safe?

FYI - It's 100 amp service in a 2000 sqft house with several breakers still available.

Reply to
Billy
Loading thread data ...

Laziness aside, is there any evidence that push in wiring is in any way less reliable or safe than wire-under-screw connections?

Reply to
Travis Jordan

Well now that you mention it, I did once see where the terminals had arched causin' the wire to burn apart and no longer make contact with the now burnt contact terminals.

Op --standin' corrected, once again--

Reply to
Guyz-N-Flyz

The dimming of the lights from the AC is unsafe?

Reply to
Billy

Reply to
Art Todesco

Dimming of lights means something carrying that startup load is not firmly connected. It could be a minor problem, it might cause incandescent bulbs to burn out faster in some parts of house, but it is definitely easily fixed, unnecessary, and maybe (only maybe) an indicator of a more serious problem.

Wires stuck in back don't bother light bulbs. But electronics need not be subjected to those intermittents and resulting failure - if wire passes through any such wired outlet.

Better electricians always wrap the wire around the screw.

Billy wrote:

Reply to
w_tom

Could it be the connection to the breaker itself?

Reply to
Billy

And sometimes, we are better off when the not-so-better wanna be "electricians" use the backwire holes. I've seen some incredibly messy, half-assed attempts at wraping a wire around a screw in my days. Not that I'm defending backwiring, but *if* you do the stripping correctly, and *if* you don't mangle the wire and insert it straight in, then backwiring can hold tight and work OK.

Reply to
Tom Pendergast

Guyz-N-Flyz rambled on about something in :

That exact thing happened at my parents. In their case, it took about 20 years to show, though...

NOI

Reply to
Thund3rstruck

Agreed. If both dome correctly, I'll take using the screws any time.

Reply to
I-zheet M'drurz

The $0.50 outlets use springs, but the better ones use clamps off the side screws. While certainly not as secure as sidescrews, they are not bad.

Reply to
Wade Lippman

Startup draws much more current than running. However, if lights dim, it suggests that the service is having trouble supplying the starting current. A poor connection in the circuit might make it difficult for the A/C to start, but it would not affect the rest of the service. (unless it is the actual service that is poorly connected, certainly a possibility)

100a is a very small service, and a 4 ton A/C is pretty big. It should say on the A/C how many running amps and starting amps it draws; how many?. Even better, invest $50 in an ampmeter and actually measure it. What else do you have going when the lights dim? If the A/C pushes the demand over 100a when starting, it will dim you lights.
Reply to
Wade Lippman

Ok...all code talk aside..

Backstabbing outlets is lazy, and can be dangerous.

Reply to
CBHvac

But why are the holes even present with a UL listed seal if they are dangerous?

Reply to
Billy

Same reason you can go buy a can of R134a with no EPA card...in UNTRAINED hands, it can be very dangerous..

Reply to
CBHvac

If the A/C pushes the demand over 100 amps, then your cooling a MALL!!

Reply to
AMEADOR

Normally, no....but it could be a sign of a loose electric connection, undersized wire, a bad compressor, or a bad cap..even a bad contactor. Depends on what you call dimming of the lights. Loose neutrals can cause this, even tho the AC unit itself wont have a neutral.

4 tons is not that large...we install 5 ton units all the time with no dimming upon startup.

Better yet, we have some 15 ton commercial units, that will start up and pull less than 60 amps upon start, and you never know they are running, and the main is only a 600 amp panel...so...you might want to have the unit checked...

Reply to
CBHvac

Are you saying it might be the unit, and not the electrical wiring? The unit is 22 years old.

Reply to
Billy

Umm...yea... See it all the time... The AVERAGE life of a unit, depending on your location, is no more than 12 to 15 years...