what is the current rating of the external 24 volt transformer

Jul 01, 2015 1 Replies
Saved reading

First reply

homeowners

2Amp fuse is actually too small for 0.5kW transformer, so it is definitely not working at the max current draw. So, what's the actual current on the secondary (24V) winding? What's the multimeter connected in series with the load show? You can try disconnecting valves and see…

Read the full reply
2Amp fuse is actually too small for 0.5kW transformer, so it is definitely not working at the max current draw. So, what's the actual current on the secondary (24V) winding? What's the multimeter connected in series with the load show? You can try disconnecting valves and see if the load goes down. Perhaps one of the valves is stuck and is, in fact, energized all the time? What's the irrigation controller you're using? Do you have the connections diagram for your installation?

Anyhow, I would start my trying to disconnect loads one by one to get to the offending one.

The transformer is made by Westinghouse (older model) rated at 120 volts and 500 watts. (.5 kilo watts) the timer seems to work properly the battery is a brand new 9 volt battery (replaced) but the problem is the transformer is getting quite warm without even any valves energized.However the fuse rated at 2 amps is ok so there should be no big current draw to heat up the transformer. What could be the problem??????


Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required