Chimney liner for oil fired boiler

Dear Readers,

I've a Burnham MPO boiler. I called Burnham, whose technicians suggest that I take the most conservative approach and line my existing exterior-wall, clay-lined brick chimney with a stainless liner to minimize flue condensation.

Should this liner necessarily be insulated as well? Or is the dead airspace (although somewhat cold due to exterior wall) in the chimney a sufficient buffer? I know the most conservative answer is to insulate the liner too, but your experiences would be appreciated as this insulation would be yet another expense on top of the liner.

Thank you very much for your responses.

-Anthony

Reply to
anthonymmfalcone
Loading thread data ...

Anthony;

Check with the Burnham Tech's again, I believe they intemnd for you to use a double wall stainless flue pipe in the chimney opening. Insulation not needed.

Reply to
Zyp

Just called them again. They expect stack temperatures of below

350F. Considering it's an exterior wall chimney and (I suggested I may also have a fresh air duct installed in the future), they once again recommend a stainless liner to prevent condensation from damaging the existing chimney. As they're not in the liner industry, they did not want to officially comment on the specific type, although the individual I spoke with said he's familiar with the single wall variety.

The double wall stainless liners I'm familiar with would seem like overkill: they are insulated in between layers and are typically the type that can be in close proximity to combustibles, like those metalbestos things. And I do not want to switch to a power vent situation.

Any 3-pass boiler (Buderus, Burnham MPO, etc) experts out there familiar with or observe a similar stainless chimney liner installation??

Reply to
anthonymmfalcone

What does the installation manual say about it?? What do your local codes require?? What did the local building inspector say about it?? What did your insurance company say about it??

We are not here to do your homework for you.

Reply to
Noon-Air

Thanks for the suggestions.

  1. Installation manual says use a liner "if condensation is observed." Per my earlier post, I called the manufacturer and didn't get too much advice on what type as it's not their product.
  2. I didn't think to check the code! Chapt 8 of Mechanical Code of NY says to use liner that will resist condensate, and is in accordance with NFPA31. I'll find NFPA31 and see what it says. Hopefully will provide guidance on insulated vs. non-insulated.
  3. Local building inspector cannot (legally) suggest anything beyond the building code, so I'll need that NFPA31.
  4. I didn't check insurance company. Not sure if they'll even understand what I'm saying. I'll try.

I have two additional thoughts:

  1. if flue gas is cooled too much within liner inside chimney, it may not create sufficient draft up the 25ft tall, exterior wall chimney. Is there a way I can estimate if I'll have sufficient draft? Reference would be appreciated.
  2. if flue gas is cooled too much and condensation occurs within the liner, is it such a big deal? It would just drip down, through the bottom tee, and into the cleanout chamber. In other words, the system would work as expected, no?

In the meanwhile, any other suggestions or experience is appreciated.

Reply to
anthonymmfalcone

So it doesn't say in the maual to use a flu chimney Type B vent? It doesn't give you a GAMA guide? Interesting.

Reply to
Zyp

Whadya want from E-Bay??? You expect to ge the install manuals too? sheesh.