Is 0.68 static pressure too high for the ECM blower on my new two stage furnace?

Oct 13, 2026 Last reply: 22 hours ago 3 Replies
Saved reading

First reply

kit.barlow_1959

0.68 on high fire with a clean filter is workable, but you're not sitting in the comfortable zone. The 1 inch rating in the manual is a ceiling, not a target, and the catch with an ECM is that it won't lose airflow as the filter loads up. It just spins harder to hold the same…

Read the full reply

Just had a 80k two stage furnace put in last week and I've been poking through the diagnostics menu on the new thermostat. On high fire the blower shows 0.68 inches of static pressure, and it drops to around 0.35 on low stage. The filter is basicly brand new, so I'm wondering how much worse this gets once it loads up with dust. A little background. Two story house, about 18 registers, and I keep a few upstairs dampers pinched back because the upstairs runs cold otherwise. I also closed two basement registers since we don't spend much time down there. I'm guessing all that balancing is part of why the number creeps up. The manual says the blower can handle up to an inch, but everything I read says ECM motors run happiest with room to spare. Should I be opening some of those dampers back up, or is 0.68 at high stage nothing to lose sleep over? The furnace spends most of the day on low anyway, where the reading looks fine to me.


0.68 on high fire with a clean filter is workable, but you're not sitting in the comfortable zone. The 1 inch rating in the manual is a ceiling, not a target, and the catch with an ECM is that it won't lose airflow as the filter loads up. It just spins harder to hold the same CFM, so the static creeps up and the motor runs hotter instead of you noticing weaker airflow like you would with an old PSC blower. That's why the headroom matters more than people think. Your low stage reading at 0.35 is genuinely fine, and if that's where it lives 90 percent of the time you're not in trouble today. But high fire kicks in on the coldest days, exactly when the motor is working its hardest, so that's the number to keep an eye on. Your balancing is almost certainly part of the number. Every register you close forces the same air through fewer openings, and that pressure has to show up somewhere. I'd start with the two basement registers since those were just extra dump zones anyway, no reason to restrict them. Then back the pinched upstairs dampers off a little at a time. Mark the positions with a sharpie before you touch anything so you can get back to where you were. Then run high fire and re-check the reading to see how much you bought back. On the filter question, don't guess how much it'll climb, just watch it. Check the diagnostic once a month as the filter ages. If you're at 0.68 clean and it's pushing 0.8 a few months in, you've learned to swap it early instead of waiting out the full season. Some filters gain pressure fast once they start loading. The CFM dial-back in the thermostat does work as a pressure relief valve, but it raises supply temps and can shorten cycles, so I'd treat that as plan B after you've opened up the ductwork. Try the dampers first, since that's fixing the actual restriction instead of masking it.

Been through this exact balancing headache on my own setup. What finally made it manageable was a cheap digital manometer, the kind that comes with the little tubing for taking duct readings. I'd tweak one damper a quarter turn, run high fire, write the number down, tweak the next one. Took an afternoon but I coud actually see wich register was buying me the most relief instead of guessing. Ended up finding one return that was undersized for the whole system, which was the real culprit. Might be worth checking if yours has a similar bottleneck before you chase dampers one by one.

One thing I learned on mine, opening the dampers only got me so far. I was chasing the supply side for weeks before I poked around the return. Mine had one undersized return grille pulling through the whole house and that was half my problem. Added a second return opening and the number dropped way more than any damper fiddling did. So if the registers only buy you a little relief, look up the return path before you settle. Also on filters, I switched to one of the lower restriction pleated ones and it made a real difference at high fire compared to the fancy allergy filter the installer left in there.