6 ft 2x6 beam - how much downward pull can it take?

Jun 13, 2012 3 Replies
Saved reading

First reply

homeowners

I'm guessing this is not for pro gym ring exercises given that the rings have to extend on their straps 3m (9.8ft) from the attachment point - not much space for that under a porch roof. This also means that you won't be creating great dynamic load on the supports (no way to…

Read the full reply

I am wanting to hang 2 gym rings from a ceiling joist. This is the only place high enough on my property to hang the rings from. The joist is a 2x6, 6' long under a porch roof. It's well secured on both ends. Would this be substantial enough?


I'm guessing this is not for pro gym ring exercises given that the rings have to extend on their straps 3m (9.8ft) from the attachment point - not much space for that under a porch roof. This also means that you won't be creating great dynamic load on the supports (no way to pull high-G swings on shorter straps, I don't think anyway) and so the load would pretty much be static and equal to your weight.

As far as 2x6 loading capacity, short spans like 6' aren't listed in the Uniform Building Code's span tables. The closest is 8'-6" and 6' would support more, so you're safe using 8'-6". Two 2x6es on 24" intervals would support 40PSF (pounds per square foot) live load (i.e. load that comes and goes such as people and furniture) plus 10 PSF of dead load (weight of the structural elements) but we won't count the dead load allowance here because the 2x6 is still a part of the porch roof support.

So the area between two 2x6, 6' long, on 2' intervals would have to be able to support 2x6x40=480 pounds of weight. Actually, slightly more since the formula is for 8'-6" spans but it just gives you a little bit of extra load for just in case.  Since you are going to hang both rings on one joist, you'd have to delete the allowance by 2, so you get 240 pounds of load uniformly spread across the 6' span. The 2x6 will deflect 6'/360=0.2" when fully loaded (span/360 is the deflection norm) which is not too bad and you probably won't notice.

Since you're still interested in gym rings I'm guessing you weigh less than the max :) .  The weight of you suspended from the rings in the center of the joist is not exactly a uniform load but the formula is, again, for 8'-6" span, so the extra strength that the shorter span affords would  even that out. Besides, the straps would have to be spaced much further apart than the standard 50 centimeters (1.6ft) if you can't have the full 3m length of the straps. You'd have to work out proper spacing yourself but whatever it is, it'll help with making this load look more like a uniform one.

In short, it looks like you should be fine!

Good luck.

You seem to be very knowledgeable about this, so maybe you can answer my question too. I also want to hang my rings off my deck/porch, but do not have a good cross beam to hang them from. I was contemplating bolting two 2x6's together to make a thicker beam and then hanging 6 ft of the beam off the end of the porch, over my yard. The beam would then be mounted to two upright beams that go from the ground up to the covered roof over the porch. Any input on this situation or recommendations for hardware? I weigh about 185 lbs.

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required