This is the oil burner safety control (model DKO 970) on my Wallstar
15/20 boiler, which once again is playing up.I downloaded the 6-page manual
In the manual on page 2 in the paragraph "1.2 Lock-out diagnoses" it says the following:
In case of a failure the LED is permanently illuminated. Every
10 seconds the illumination is interrupted by a flash code, which indicates the cause of the error. Therefore the following sequence is performed which is repeated as long as the unit is not reset.Sequence:
illuminated phase dark phase Flash-Code dark phase x z z z z
[where illuminated phase = 10 sec, dark phase = 0.6 sec, second dark phase = 1.2 sec -- I can't fit all that on one line in FreeAgent like in the actual PDF]Error diagnosis Error message: lockout Flash-Code: x z z z z Possible fault: within lock out safety time no flame establishment
[where x = short pulse, z = long pulse]This is the sequence I observe on my boiler when it won't start.
So my question is:
What does "within lock out safety time no flame establishment" mean in layman's language?
Does this point to the burner, the igniter, the solenoid, or another component?
NB: The boiler ALWAYS starts when I press the reset button on the DKO
970. I never have to press it more than once. The boiler then runs perfectly, cycling through on/off phases exactly as it should.But next morning it won't start and the above flash code sequence can be observed. There's plenty of oil in the tank.
Thanks.
MM