Is a 25' run of 15mm supply pipe acceptable for a new boiler? Thats gas supply, not electric :)
I need to know fairly quickly this time. Boiler power 30-40 whatnots
thank you, NT
Is a 25' run of 15mm supply pipe acceptable for a new boiler? Thats gas supply, not electric :)
I need to know fairly quickly this time. Boiler power 30-40 whatnots
thank you, NT
No It would not be acceptable for an older boiler
Kilowatts? If so, then almost certainly no.
Doubt it. My boiler's about 18 whatnots and the manufacturers specify
22mm pipe to within about 12 or 18" of the boiler. There might be something similarly specified in the installation manual for your boiler. You can't calculate the pressure drop (which is usually the criteria) without details of all the other appliances, pipe lengths, tees, etc..
No, if you mean kW. It might be OK for kBTus (an ancient unit), but calculations might be in order even then.
Christian.
If you have a look here
Alex
Thanks to everyone :) I am pretty ignorant on this, but assumed its kbtus. Its probably 30 odd years old. The 15mm supply has never been a problem in any way, but thats bureaucracy for you.
So I guess I'll have to run a 2nd pipe in parallel to lower the resistance. I've got an old hose reel somewhere...
NT
I bet someone'll be hooked - but who will it be?
If it has worked perfectly for 30 years, then leave it, unless it has failed an inspection. Without doing the calcs, and assuming few elbows, the run is probably just below spec. Perhaps someone will be kind enough to do the calcs for you!
Christian.
Yep, its failed. A new run it is - wont be hard to do. Its the new boiler I'm unhappy about.
Oh, yes there was another appliance run off that section of pipe too. I guess I had modulation and didnt know it :)
cheers, NT
Ah. Another appliance will drop it much lower!
If the other appliance is greedy, you might even need 28mm to the split and
22mm after. There's no point in underspeccing the new run. Your next boiler might be a 40kW monster.Christian.
Well if you take a m^3 of gas as 37MJ, assume the boiler is 40k BTU (11kW ish) that gives you 11000*3600 J / hour, or about 40MJ. So that is a gas rate of approx 1.1 m^3 / hour.