Wiring query--I've got a mental block it seems...

Page 1 of 2  
Taken from old silo unloader to use as second parallel from alternate location DC in shop...
240V coil relay, 240V 2hp-rated contacts of the mechanical spring type--load contacts a common and one open/one closed pair. Relay operates by momentary make/break--when cycled, the spring-loaded contacts switch positions rather than by being held by continuous load.
Switch is manual pushbotton, START is NO, STOP is NC and one side of each are common.
The wiring on the unloader was so decrepit I didn't try to trace it out when salvaging pieces/parts but I'll be darned if I can figure out how Dad had this wired to work (but I know it did, I was around for years while still were using it and it was sitting there as was removed and parked).
I can see how to get the START to work, what I haven't got my head around is the STOP function since it breaks a contact instead of makes one to cause the relay coil to momentarily energize/release to flip the spring-loaded contacts...
I'll see if I can manage an ASCII pictogram here...
X C X Contacts (C common) / / |
Coil L1-\/\-L2
x____x START / | \x x STOP ____
Anybody draw a schematic to start/stop a load across an X-C pair? There's a jumper from L2 to C for starters for supply...
--



Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Tue, 19 Jun 2012 12:19:44 -0700 (PDT), " snipped-for-privacy@optonline.net"

Help us out. Just take pictures.
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/19/2012 2:49 PM, Metspitzer wrote: ...

Of what, specifically do want a picture?
All I can take a picture of would be the face of the relay in the box and it'll show 3 relay contact screws at the top and the two coil connections (plus the jumper from one of them to the common terminal of the output contacts).
It's an old Furnas contactor and Furnas is, of course, long gone. AFAICT there's no part number to try to find old stock or reference diagrams from...
--



Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

https://www.google.com/search?hl=en&safe=off&client=firefox-a&hs=PIQ&rls=org.mozilla:en-US:official&channel=np&q=start+stop&bav=on.2,or.r_gc.r_pw.r_cp.r_qf.,cf.osb&biw 16&bihY3&um=1&ie=UTF-8&tbm=isch&source=og&sa=N&tab=wi&eimfgT46KEY6c8QS36uT5DA#um=1&hl=en&safe=off&client=firefox-a&hs=Byk&rls=org.mozilla:en-US%3Aofficial&channel=np&tbm=isch&sa=1&q=start+stop+diagram&oq=start+stop+diagram&aq=f&aqi=g1g-mS2&aql=&gs_l=img.3..0j0i5i24l2.9766.11941.0.12357.8.8.0.0.0.1.888.1427.7j6-1.8.0...0.0.wbuTYf1s24c&pbx=1&bav=on.2,or.r_gc.r_pw.r_cp.r_qf.,cf.osb&fpøeb300daecb8750&biw16&bihY3
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/19/2012 2:52 PM, Metspitzer wrote: ...

Thanks, that shows a bunch of schematics indeed--I'll try to work through and see if anything seems to fit.
The diagram at <
http://sub.allaboutcircuits.com/images/04176.png is good when the relay is powered to hold the relay contacts closed but the kicker in this case that has me puzzled is that the contacts change position only when the coil is energized/de-energized because they're spring-loaded and it's the spring action when the coil de-energizes that causes them to switch position, not the coil magnetic field causing an actuator to move...
The switch is similar to
<http://www.automationdirect.com/adc/Overview/Catalog/Pushbuttons_ -
z-_Switches_-z-_Indicators/Eaton_Cutler-Hammer_22mm_%28E22_Series%29
/Start_-z-_Stop_Combos_-a-_Stations>
just a normal manual switch as shown in the above schematic as well w/ the one side of Start/Stop connected as shown there to be in series.
It's clear to get a coil pulse thru the coil to press "Start"; what's got me is then if the coil stays energized the contacts don't switch position to actually start the motor.
'Tis a puzzle (to me, at least at the moment still)...
I'm sure at some point the light will dawn and I'll be realizing how silly I've been in not seeing the obvious... :)
--
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/19/2012 3:54 PM, dpb wrote: ...

Well, of course the magnetic field does cause the actuator to move, the thing is when it moves in the contacts don't move; they only change position on power removal when the spring action causes the contact changeover.
As noted in reponse earlier to follow up to Ralph I just went and confirmed the mode of operation w/ a test cord...
--
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Look up a 3 wire stop start circuit. The stop button contacts are normally closed. The start button will be normally open. A set of normally open contacts from the coil are in parallel with the start button. When you push the start button the coil pulls in and the contacts parallel the start button to simulate keeping it pressed. When you press the stop button, the coil looses power and drops out the contacts in parallel with the start button.
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/19/2012 3:23 PM, Ralph Mowery wrote: ...

Excepting for the kicker on this relay that the contacts only actually switch on a pulse instead of on/off--they're spring loaded and it's the spring action when the coil de-energizes that causes them to actually change position--they don't on power-on only.
So, I can start it w/ the momentary but can't figure out how to generate the pulse w/ the NC Stop contacts.
I initially thought both were NO until I went to wire it up this morning and discovered that isn't so and what I thought it was doesn't work...
--
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/19/2012 3:58 PM, dpb wrote:

And, I just wired up a test cord to make certain I wasn't seeing something I wasn't--that is precisely how it operates...
Head scratchin' time a little longer here...
--
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Tue, 19 Jun 2012 19:56:43 -0500, dpb wrote:

The contactor has an auxiliary contact for control voltage that is NO and makes up with the pulling in of the main contacts.
control power hot goes into one side of the stop switch (nc) and is jumped to one side of the start switch (no), the other side of the stop switch goes to the auxiliary contact, the other side of the start switch goes to the other side of the auxiliary contacts and is jumped from the auxiliary to the coil of the contactor.
the other side of the coil is connected to the overload contact relay, withe the neutral hooked to the other connection of the overload relay.
The start switch temporarily supplies power to the coil until the power can come through the auxiliary switch, the stop switch breaks the circuit and allows the contactor to drop out.
If I remember correctly the auxiliary contacts on a furnas are built along side the main contacts. There will be two small connections at the bottom behind the motor leads that are the overload contact relay.
basilisk
--
A wink is as good as a nod to a blind horse

Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/19/2012 5:56 PM, dpb wrote:

relay?
I think that it will work. The Start button energizes the coil. When the Start button is released the coil is de-energized. Then the relay toggles and power is sent to the load. That also allows current to be sent back to the coil via the normally closed contact of the Stop button. However the relay stays in its same position (i.e. still sending power to the load) until the current to the coil is interrupted. This happens when the Stop button is pressed.
Even though this relay does not need to have it coil energized during normal run operation, it would be in this case. Hopefully this does not cause the coil to over heat. Since you said that your father used this arrangement for years, I am guessing that this is not a problem.
A loss of input power while running would also toggle off the relay. That is a nice safety feature.
/ / Line C / NO LOAD ------+-------O/ O-------+---------------- | | | | +--* | +--*| | Start | Stop +--* | +--*| | | | | +---------+------------+ | * L1 | Coil | * L2 Neutral | ----------------+-----------------------------
Dan
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/19/2012 10:34 PM, Dan Coby wrote: ...

That may be (probably was?) the way it was; it's too long ago that I have no way of knowing. I can give it a try; I did notice it's pretty noisy when actuated altho in the silo 50 ft in the air w/ the unloader fan running who would have noticed? :) It won't take long to see how much heat it dissipates altho I've only cycled it in playing around so far.
It's a 240V coil; I tried it w/ 120V and it doesn't have enough oomph to move it so it's both hot legs instead of a neutral/hot, but that's a detail; the path is the same if your supposition is right (that that's the way it had been used and I've been trying to make it more complicated than it was, not that it won't work). I just had a mindset when I started that it was only momentary and kept trying to work around that idea that just doesn't seem that can be (or ever was so)...
Appreciate the input from all; anybody gets any more really clever/strange ideas... :)
--
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

running????? AND it uses a NO and an NC switch??? Sounds fishy to me. A "galopping ghost" relay starts with one pulse and stops with a second pulse - a modification of that circuit uses 2 separate NO switches and a spdt pilot switch to select which switch sends the pulse.
GENERALLY a NO/NC pushbutton starter uses an electrical "latching relay" circuit, the ON button momentarily closes the relay, and the pilot contacts of the relay close the circuit to the relay by bypassing the ON switch, with current flowing through the NC OFF switch. By pressing the OFF switch the circuit to the coil is broken, the relay opens, and the pilot contacts also open. To restart, control voltage is applied to the coil through the normally closed off switch and the pressed normally open ON switch, which pulls in the contacts of the relay to start the motor as well as the pilot contacts, which hold the coil in when the ON switch is released.
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/19/2012 9:16 PM, snipped-for-privacy@snyder.on.ca wrote: ...

Those are the pieces parts that were in use, yes...

Well, until I started wiring I had presumed the switch was to NO to do precisely that--a start and a stop pulse and was in process when realized wasn't so...

And now you see why I am left puzzled how Dad had this working on the old unloader from which I took the pieces... :) I'm virtually positive it hadn't been touched since last time it was pulled out of the silo and set in the corner for the auction (but it didn't sell; by then nobody else was filling upright silos anymore, either). So, I figured might as well use the parts for something...
If I can't dream up what he did tomorrow, guess I'll rummage around for something else and figure out another workaround -- it just bugs me that somehow this seemed to have been working before. I wish now I had tried to trace out the old wiring more carefully, but that ship has sailed at this point...
--
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

If it really operated the way you described (the main relay coil was pulsed), it would have required a second pilot relay to work with a N.O. stop button.
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Wed, 20 Jun 2012 10:23:00 -0400, snipped-for-privacy@carploin.com wrote:

Sorry - Make that "to work with a N.C stop button."
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/20/2012 9:53 AM, snipped-for-privacy@carploin.com wrote:

Indeed, seemed that way to me...so thought was I'd ask if I was missing the obvious.
Turns out I was.... :)
Overnight was puzzling this over and indeed I had made an erroneous conclusion earlier. I had thought this switch/relay was controlling the blower motor directly and the larger auger/propulsion drive motors were on a separate control so could use this to clear it. But the obvious problem in wiring it this discussion has clarified got me to go and look again this morning and it turns out when I opened that other box they were all three in there after all and this relay is simply the intermediary for that contactor and the off function drops out the hold in relay that is in that other box...so there was a second cable I'd forgotten was there when I just picked up these pieces that I had stripped earlier.
So the mystery turns out to be no mystery after all but the parts aren't nearly as convenient for my present purpose, either, unfortunately...
Since this is just the one small motor well within the contact rating of this relay and I'm the only one around, I may just go ahead and use a large-enough wire for the jumper to common and power it thru this and just use the START button as both start and stop. It's just the DC, so it's not like it was the TS or somesuch...
There's a bunch of other old gear out in the barn I've not even sorted through since been back; maybe I can find something else to make it a little less bulky than what this was driving in its earlier life...
Anyway, thanks for the input from all...
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/20/2012 10:46 AM, dpb wrote:

Glad you figured it out. I have certainly had problems making wrong assumptions and trying to figure out how something worked.
For what it is worth, the DC ratings of contacts are not the same as the AC ratings. DC tends to arc. AC contacts get help from the zero crossings of a sine wave.
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/20/2012 1:52 PM, dpb wrote:

Dust collector sounds better than DC voltage.
Motor start current is about 6x run current. Would be nice if the contactor had a HP rating.
As I understand the contactor it changes when the coil is deenergized. This circuit should work:
230 start | _____ 230 | | | /x__________o o___________________ coil ________| | / | | |_____C/ | | | _____ | | | | | | x__________o o________| | | | | | contactor | stop | | | | |_______________________________dust col ____|
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 6/21/2012 12:50 PM, bud-- wrote:

Pulsed, more accurately...but on the deenergize cycle of that, yes.

reflect what is present]...
230 start | _____ 230 | | | /x__________o o___________________ coil ________| | / | | |_____C/ | | | | | | _____ | | | x__________o o________| | | | | | contactor | stop | | | | |_______________________________dust col ____|
Yes, it would if the Start/Stop were both NO but the Stop is NC as represented above. That would leave the coil energized during run and no way to deenergize it.
The only way w/o a second relay I can see could work would be to simply use the START button as a cycle ON|OFF and forget STOP. (NB my followup earlier that mentions that after an overnight I went and looked at the other large box that I remembered only having the motor-protect fuses in it and "discovered" the missing relay there...inconvenient for my present purpose but explained the mystery of how the silo unloader worked previously.
--