Because of a specific problem, I picked up a combination SPST switch and GFCI single outlet with a "load" connection.
Anyway, the instructions clearly say that one should NOT use the switch to control the input to the GFCI.
Why should that be a problem?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

If what you have is similar to the Leviton brand that I buy, it may be that the switch rating is lower than the outlet rating. Just a guess, but it seems like the switch is pretty light duty.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
If you use the switch to cut power to the outlet, then you will also be switching off everything down stream (connected to the "Load" side of the device. You would need to be sure that the switch is rated for 15 or 20 amps depending on the rating of the circuit you are installing it on.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@aol.com wrote:

Hi, As a result GFCI may trip.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 8/29/2009 8:09 AM John Gilmer spake thus:

Where did he get that idea?
That one doesn't even pass the common-sense test. If a device is rated for 15 amps, how is it OK to use it on a circuit drawing (potentially) 20 amps?
Now, I could see using a 15 amp switch on a 15-amp circuit (meaning one connected to a 15 amp breaker) but wired with #12 wire. Is that what the electrician meant?
--
Found--the gene that causes belief in genetic determinism

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Well, there seem to be some special rules for 15/20 amp stuff. For example, a 15 amp outlet can "pass thru" juice to a 20 amp outlet. A 15 amp outlet can be on a 20 amp circuit.

Nope!
I implied by error the conversation I had was recent. It actually took place about 2 years ago. I had some switched outlets and I couldn't find 20 amp SPST switches. That's when he told me I could put 15 amp rated switches on a 20 amp #12 wire circuit.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I am not a real expert on the subject but I do not see the problem. Very few lights would even come close to requiring 15 A. A fixture containing three 100 watt lamps requires less than three A on a 120 V power line (neglecting inrush current). You can always screw things up by placing an overload exceeding 20 even if had 20 A switches.
Electrical codes can be arbitrary, but I would be surprised if all parts of a circuit must always be matched to each other.
Bill
--
Private Profit; Public Poop! Avoid collateral windfall!

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

We have a winner!! You can't put a single 15 amp outlet on a 20 amp circuit, because the potential to overload it, and by the same logic, you wouldn't put a 10 amp or 15 amp switch on a load greater than the switch capacity, but you certainly can install a 15 amp switch on a bank of lights that draws 10 amps, which is fed off of a 20 amp circuit.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Can we extend that logic to say that you can put a 15 amp switch on a "bank" of 15 amp outlets?

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
RBM wrote:

Aren't we talking about a receptacle here? It may be intended for a lamp, but that doesn't mean that's what will get plugged into it. If the switch is 15A feeding a receptacle, I would at the very least split the duplex so that only one side is controlled by the switch, otherwise there is potential for a greater than 15A load.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
RBM wrote:

I agree.
The NEC requires "switches shall be used within their ratings".
IMHO a 15A switch on 20A circuit with 20A or multiple 15A receptacles would be a violation.
-- bud--
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

This is one of the many NEC rules that make no sense to me. The same thing with multiple disconnects on a service, the original installer may have calculated the load, but who knows about any subsequent installations and installers
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
RBM wrote:

>>>

>>

The way I read the thread I was agreeing with you. A 20A circuit with a 10A switch for a lighting fixture is OK because it is substantially impossible to put over 1200W of lights in. Switching an outlet is more of a problem.
Multiple service disconnects could certainly be a problem - they are a lot safer if non-electricians leave them alone. IMHO most of the potential problems are "split-bus" panels in a house. My reading of the code is they are still allowed but I don't know if anyone even makes them anymore.
--
bud--

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

I understand that, it is in switching an outlet that I have the concern. I don't believe there is any rule to disallow a 15 amp switch on , say a single duplex outlet in a bedroom, that's fed from a 20 amp circuit. While it's unlikely that the switch would be overloaded, why not just require the switch ampacity to match the circuit, instead of what's being switched

That's exactly what I'm talking about. I run into the damn things all the time. You go to a house to install an outlet for a microwave, check the panel, it's a split buss with a total of 250 amps worth of mains on #2 AL. Then you have to do a load calculation of the whole house and make sure your liability is paid up, before you add the one stupid outlet

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Bud They are effectively forbidden by the requirement that "Each lighting and appliance branch-circuit panelboard shall be individually protected on the supply side by not more than two main circuit breakers or two sets of fuses having a combined rating not greater than that of the panelboard." -- Tom Horne
408.14 Classification of Panelboards. Panelboards shall be classified for the purposes of this article as either lighting and appliance branch-circuit panelboards or power panelboards, based on their content. A lighting and appliance branch circuit is a branch circuit that has a connection to the neutral of the panelboard and that has overcurrent protection of 30 amperes or less in one or more conductors. (A) Lighting and Appliance Branch-Circuit Panelboard. A lighting and appliance branch-circuit panelboard is one having more than 10 percent of its overcurrent devices protecting lighting and appliance branch circuits. (B) Power Panelboard. A power panelboard is one having 10 percent or fewer of its overcurrent devices protecting lighting and appliance branch circuits.
408.16 Overcurrent Protection. (A) Lighting and Appliance Branch-Circuit Panelboard Individually Protected. Each lighting and appliance branch-circuit panelboard shall be individually protected on the supply side by not more than two main circuit breakers or two sets of fuses having a combined rating not greater than that of the panelboard. Exception No. 1: Individual protection for a lighting and appliance panelboard shall not be required if the panelboard feeder has overcurrent protection not greater than the rating of the panelboard.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

The notion of lighting and appliance panelboard has been removed from the 2008 NEC.
Cheers, Wayne
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Tom Horne wrote:

Wayne is right that "lighting and appliance panelboards" disappeared in the 2008 NEC. You are quoting a NEC version before 2005 (but 2005 probably said the same thing, relocated).
The 2008 NEC also has the same requirements, I believe, as what you quoted, with the 42 pole limit moved into the main article text, which is 408.36 exception 2.                          My reading is that you can have a split bus panel, but that there can only be 2 main circuit breakers (instead of the previous 6). (One breaker feeds the split bus in the rest of the panel and the 2nd breaker can feed your flying saucer port on the roof.) The sum of the main breaker ratings has to be not greater than the panelboard rating, but there is nothing in this article that I see that prevents the 2 devices from having a rating larger than the service wires using the 6 disconnect rule.
IMHO this is one of the articles where it would help to be a lawyer. (Or maybe not.) You might have used a different lawyer?
--
bud--

>
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Switches need only be adequate for the load that they control. It is very common in US practice to use ten ampere switches on fifteen ampere circuits and there is nothing wrong with that as long as the load to be controlled does not exceed the rating of the switch. Switches controlling receptacle outlets should never be less than the rating of the circuit because the cord and plug connected load could well be the entire ampacity of the circuit. -- Tom Horne
404.14 Rating and Use of Snap Switches. Snap switches shall be used within their ratings and as indicated in 404.14(A) through (D).
(A) Alternating Current General-Use Snap Switch. A form of general-use snap switch suitable only for use on ac circuits for controlling the following: (1)    Resistive and inductive loads, including electric-discharge lamps, not exceeding the ampere rating of the switch at the voltage involved (2)    Tungsten-filament lamp loads not exceeding the ampere rating of the switch at 120 volts (3)    Motor loads not exceeding 80 percent of the ampere rating of the switch at its rated voltage (B) Alternating-Current or Direct-Current General-Use Snap Switch. A form of general-use snap switch suitable for use on either ac or dc circuits for controlling the following: (1)    Resistive loads not exceeding the ampere rating of the switch at the voltage applied. (2)    Inductive loads not exceeding 50 percent of the ampere rating of the switch at the applied voltage. Switches rated in horsepower are suitable for controlling motor loads within their rating at the voltage applied. (3)    Tungsten-filament lamp loads not exceeding the ampere rating of the switch at the applied voltage if T-rated.