Hi all:
Six years ago, I built my workshop about 150ft from the house with a 100A service. I ran a four-conductor cable to the subpanel in the shop, and kept the ground and neutral conductors isolated from each other. I did not bond the sub-panel ground to its own ground rod, thinking it might cause a ground loop and/or noise in the intercom circuit bewteen the buildings. More recently, when I put in a spa with it's own GFCI breaker, I had several people advise me to drive a separate ground rod for it, and that I should have done the same for my workshop. So far, I have had no issues, but I want to make sure I did the right thing.
My searches here have yielded many debates on the need to keep the ground and neutral bonded only in the main panel and not the subs (which is how I did it), but nothing about the ground rod question. Does a remote subpanel need its own ground rod or not? Thanks in advance, John.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Yup you need a ground rod and that gets connected to the ground bus, The neutral still stays isolated
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

2002NEC 250.32(b)2
Paraphrase, if you have no grounding method between your main panel and the garage panel, then you bond your sub panels grounded(neutral) and grounding conductors in the sub panel.

2002NEC 25.32(A) Exception
Paraphase:if you have only one branch circuit supplies your subpanel, and it has an equipment grounding conductor, then you are ok without the ground rod.

No debate, all in black and white in the blessed book. :-P
hth,
tom @ www.FreelancingProjects.com
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Would a seperate ground cause a difference of potential ? Causing a hazzard?

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Unless you have a connection between your garage and main dwelling such as water pipe, you need to install a ground rod for your sub panel. You don't need to put in a ground rod to your spa. You do, however, need to bond any grounded metal within 5' of the spa water to the bonding lug on your spa panel, using bare solid copper.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Supplemental grounding gets tricky pretty fast. Excellent choice for the 4 wire service to the garage. Now if you drive a ground rod at the garage then the grounding conductor back to the service must be of the same size as your service ground. If not you COULD have a problem with an fault.... note could.. As for the spa driving another ground rod is just complicating the issue. I assume that you took a grounding conductor to the spa, if it is connected correctly you do not need a ground rod there. Try reading the Soars book on Grounding. Lots of pictures and easy text to understand. Heck I probably do not understand what your doing cause I can not see it.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
SQLit wrote:

If he ran a 100A feeder to the garage panel, the grounding wire is at least 6 gauge, and maybe 4. IIRC, #6 is the largest wire you are ever required to use to connect a ground rod to the grounding electrode system.
I would probably drive a ground rod at the garage. I don't know if it is required or not (but I think it is.) Since there's a seperate grounding wire already, I don't think it's all that important.
Bob
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

thought 6 was small, so went looking. 2002nec table 250.66 for copper 3/0 is the largest, and for aluminum 250 kcmils. They are a little bigger than 6awg.

Good point, it doesn't seem to be anything against driving another grounding rod, but then, if he wired it correctly, nothing seems to indicate he needs to.

imho,
tom @ www.WorkAtHomePlans.com
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@intertainia.com wrote:

(I wish I could find my code book, even though it's 10 years old.) I don't think NEC ever requires a conductor that big to connect a ground rod to the electrode grounding system. In fact, I think there is a specific exception that says it never has to be larger than #6 copper or #6 copper-clad aluminum. It probably does require an equipment grounding conductor (ground wire), or grounded conductor (neutral wire) that big for 200A or larger feeder circuits, but that's not what we are talking about.

Bob
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Right on Bob The GEC to a "made electrode" (rod or plate) does never have to be bigger than #6 copper
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Since you ran a grounding conductor with the feed to the subpanel, you do not need to install a ground rod at that location.
If you feel the need to install a ground rod it should be at the main panel. What is your current main ground?
John Grabowski http://www.mrelectrician.tv

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Simply not true. Anything beyond a single branch circuit to a remote building requires a ground electrode system. The only thing a 3 wire vs 4 wire feeder affects is regrounding the neutral at the remote building. http://members.aol.com./gfretwell/subpanel/bdg2subpanel.htm
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Greg, I think you misinterpreted the pictures as indicating a ground rod for each panel. The grounding symbol is used to only illustrate a common ground. Read the text and you will see that an additional grounding electrode is not required if a grounding electrode conductor was run with the service feeder.
The original poster did the job correctly by running four wires and keeping his grounding conductor separate from his grounded conductor (Neutral).

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
John Grabowski wrote:

Sorry John but that is bad information.
Every building that has more than a branch circuit to supply it has to have a grounding electrode system. That can be as little as a single ground rod if it has an impedance to ground of twenty five ohms or less. If the impedance of the single rod is higher you have to add a second rod. Most electricians do not bother to measure it and just add a second rod. If the building already has an electrode such as a concrete encased electrode then you only have to bond the service equipment enclosure to it and your done. In all cases each separate building gets a grounding electrode system. There are no exceptions under the US NEC. The objective is to "limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines" and "stabilize the voltage to earth during normal operation."
250.50 Grounding Electrode System. If available on the premises at each building or structure served, each item in 250.52(A)(1) through (A)(6) shall be bonded together to form the grounding electrode system. Where none of these electrodes are available, one or more of the electrodes specified in 250.52(A)(4) through (A)(7) shall be installed and used. Copyright 2002 National Fire Protection Association.
In short every building 1) needs a grounding electrode system if it is supplied with more than a branch circuit. 2)The building disconnecting means gets bonded to the grounding electrode system. -- Tom H
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Tom, I agree that each building needs to be connected to the grounding electrode system. However my interpretation is that the grounding electrode system originates at the main service entrance and can be extended to secondary buildings along with the power. Therefore a ground rod at each secondary building is not necessary as long as the building components (Metal piping, steel, subpanel, etc.) are bonded to the grounding electrode system that originates from the main service.
I seem to recall an article from a few years ago in one of the trade magazines that discussed this issue of multiple grounding along a distribution system. I think one of the problems is that it is possible that the ground rod in a secondary building could have less resistance than the primary ground rod (Or water pipe). Since electricity follows the path of least resistance it is possible that the loss of a neutral could have current travel away from the main service to a secondary building's ground rod. Anyway, my memory isn't that great. I could be mistaken.
John G.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
John Grabowski wrote:

John We can talk what ifs until the cows come home. The requirement in the US NEC is plain. If the building is supplied by a feeder rather than by a branch circuit it must have a grounding electrode system and the building disconnecting means must be bonded to it. It makes no difference whether there is or is not an Equipment Grounding conductor run with the feeder a grounding electrode system is still required at each building. Which conductor of the feeder gets bonded to the Grounding Electrode System at each building is dependent on whether there is an EGC in the feeder. Either way you must bond the building disconnecting means to a grounding electrode at the building that the building disconnecting means serves. The US NEC does not allow any other course of action. -- Tom H
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Tom, I believe in this particular instance that the feed to the subpanel is a branch circuit even though the owner is calling it a service.
wrote in message

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
John Grabowski wrote:

John Any circuit that starts at one Over Current Protective Device (OCPD) and supplies other OCPDs is by definition a feeder vis.
ARTICLE 100 Definitions... Feeder. All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device...
Since the "final branch-circuit overcurrent device" are the circuit breakers that protect the branch circuits which are located in the panel in the garage the circuit that supplies that panel is a feeder. The exception in the NEC is meant to exempt small sheds or out buildings that are literally supplied by a branch circuit. To be a branch circuit the last OCPD has to be at it's source.
Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).
That exception that exempts buildings supplied by a branch circuit from the requirement for a grounding electrode system has a companion exception that exempts such buildings on residential property from having a building disconnecting means that is listed as "Suitable for Use as Service Equipment" The exception says
225.36 Suitable for Service Equipment. The disconnecting means specified in 225.31 shall be suitable for use as service equipment. Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.
When taken together the requirements for buildings that are supplied from a service that is located in another building come down to all buildings must have a disconnecting means. All buildings supplied by a feeder or service must have a grounding electrode system. The disconnecting means must be bonded to the grounding electrode system by a properly sized Grounding Electrode Conductor.
I am not being so insistent in order to be argumentative but rather because I don't want neophyte DIYs to follow unclear or misguided advice and come to harm. -- Tom H
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Tom, I think that we have confused everyone who is following this thread enough so I will end it here. I will be attending a grounding and bonding class in a few weeks as part of my continuing education requirements. I will certainly be bringing this issue up in that class.
Out of curiosity a question for everyone: Is the original poster required by 2002 NEC standards to install a ground rod at his subpanel location? YES or NO, no more discussion PLEASE! :-)
John Grabowski http://www.mrelectrician.tv
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 15 Jan 2005 19:22:59 -0500, "John Grabowski"

Maybe.
Sorry couldn't resist.
:-P
later,
tom @ www.FindMeShelter.com
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Related Threads