Circuit Breaker

I have a 15amp circuit breaker from my main panel going to my garage panel. The wire going to the panel to the garage is 10awg. I was wondering if i could change that circuit breaker to a higher one. I have a 220V heater that is 20 amps that keeps tripping the 15 amp breaker on the main panel. Could I go to a 30amp breaker on the main panel to the garage? On the garage panel there is 2 15amp circuits and the 2pole 20amp circuit for the heater.

Thanks Stuart

Reply to
stumarshall
Loading thread data ...

Probably. Naturally you will want to be certain there is nothing on the circuit that can't handle 30a; though I can't think of what there could be... You also have to figure out how long the cable is, what the load is, and the voltage drop. Do a search on VD calculators. If the only load on it is the heater and some lights, VD isn't all that important. If you have motors or electronics, much more so. In short, there could have been a good reason for the 15a breaker; make darn sure there wasn't before changing it.

Reply to
Toller

The reason of the 15 amp breaker on the main panel was that when they put in the garage panel it only had the 2 15amp circuits (one for the lights and one for the outlets). I got the electrican to put in the

240V 20amp circuit a few years later for the heater. So would i need a 30amp circuit breaker going to the garage or could i go with a 20amp breaker
Reply to
stumarshall

You have to consider what I said above. If you have a very long cable run, you could get bad voltage drop on big loads. A 20a breaker will stop you from having big loads, and thus prevent VD. If your run is short, or you don't care about VD, then a 30a breaker will be fine.

Now, I am saying that without seeing the circuit! I can't think of any reasons that would prevent you from using a 30a breaker, but that doesn't mean there aren't any that someone actually looking at it would see.

Your electrician was pretty dim to put a 20a heater on a 15a circuit. Perhaps he did other dim things. (mostly covering my ass here, but it is possible...)

Reply to
Toller

A #10 wire is good for 30 Amps, though you would need #10/3 to get your 220v for the heater. The breaker would be a 2 Pole Breaker (either a Double, or a Quad with the inner/outer connected.

Like Toller mentioned. Make sure that the #10 from Breaker to Panel is the only thing that connects the two panels together. Does the Garage have a Main or is it wired into lugs at the top of the panel? Should be wired into Lugs and the panel should be rated for the 30amps or better.

Scott

Reply to
Scott Townsend

Reply to
stumarshall

Stu:

First, I am not an electrician, just a homeowner who isn't afraid to read the NEC manual when I need to. Take what I tell you with a grain of salt, and confirm it with an experienced electrician.

Okay...the NEC does not *restrict* us to a maximum voltage drop (at least for residential wiring) but does recommend a maximum of 3% on a branch or feeder and 5% on branch & feeder combined, and leaves it up to the AHJ, but let's go by their recommendation for fun. Your 10awg run from the 15A breaker is a feeder.

If you put this subpanel on a 30A DP breaker, your worst case for voltage drop would be a 30A 120V load, because 3% of 120V is less than 3% of

240V. All current would then be flowing out one hot conductor, and back down the neutral.

Voltage drop allowed:

F = Length of feeder ((hot length + neutral length)/2) E = IR (Ohm's Law)

E = 3.6V (3 of 120V) R = .0012 ohm/ft (resistance of 10AWG = 1.2 ohm/ 1000ft) I = 30A (max current)

E = 30 * .0012 * (2*F) = F