The summer project of adding a multi-fuel thermal store, new gas boiler & Wood Burner boiler is now providing hot water and heating, Wood burner still to fit but I believe the store might be thermo siphoning through the boiler causing a temp. drop from 60 degrees to around 50 degrees overnight when the boiler is deactivated.
Due to it's location the new Intergas heat only boiler is close to the ceiling so the top of the boiler is higher than the top of the thermal store by about a metre. Flow and return pipes exit the boiler at the top so they run over the flue next to the ceiling then drop down the wall and across to the thermal store tap-off points. Flow is right at the top of the store and return is around
2/3rds of the way down the store where it goes into boiler pump then back up to top of boiler.All formerly hot pipes have been lagged as they were leaking heat from the store but the boiler case seems to remain warm. (around 30 to 35 degrees, much the same as the insulated pipes.
THe boiler thermostat is the same height as the return pipe to the boiler and set at 60 degrees which still gves more than enough DHW for 2 people mixed down to 55 degrees.
The Intergas boiler heat exchanger is a big slab of Aluminium which the water wiggles throughfrom bottom to top so I'm now suspecting that the heat exchanger is working in reverse when the pump isn't running, transferring heat from the non-pumped system water to the inside of the boiler.
Does this sound plausible? I've found references to a "London Loop" where the DHW pipe on a hot water tank is taken down the cylinder before returning back up into the loft or wherever.
Am I being overly concerend? Let's say for example the boiler and connecting pipes have become "part" of the thermal store, and heat is leaking from the boiler heat exchanger into the case of the boiler and potentially out through the flue, is this still likely to happen if I dropped a loop in the flow and return pipes down to the floor before going back up to the boiler?
From my understanding, although thermal siphoning by convection might be reduced by a downward loop heat can still travel downwards through the water by conduction both of the water and the copper pipe all be-it at a slower rate.
Other than that the store takes around 20 to 30 minutes to recharge to
60 degrees after 2 full showers with the boiler set to an output temp. of 70 degrees.Right, more importantly for me now is to get the woodburner/boiler plumbed in and a flue fitted before gas prices go up again!
Thanks for your thoughts as always (those that I can see). Cheers - Pete