Our immersion heater has just stopped working. The heater itself is
> not open-circuit, and the thermostat appears to be working. It's a
> fairly old immersion, so there's no over-temperature or backup
> thermostat. Investigation suggests that the relay in the electronic
> time switch has failed, because although there's a click when it comes
> on, there are no or only momentary volts on the output terminals of
> the timer. It's rated at 3kW.
>
> The resistance of the immersion heater itself is 12.8 ohms, measured
> with a simple electronic multimeter. Some simple maths suggests that
> with 240 volts applied, a resistive load of this amount would draw
> 18.75 amps, and be dissipating 4.5kW, i.e. half as much again as the
> rating of the time switch, even though the cover-cap on the immersion
> clearly says it's a 3kW immersion. If my measurements and calculations
> are correct, it would explain why the relay on the time switch has
> failed. But do/did 4.5kW immersion heaters exist, or could the
> resistance have fallen over time (seems unlikely to me, though)? If
> it's genuinely a 4.5kW heater, are time switches available rated at
> that wattage? I've only ever seen 3kW ones.
>
> Fortunately, we can also heat the water with gas (propane) via a
> Vaillant boiler, but off-peak electricity is cheaper.
Don't forget that the reistance of the increases when it gets hot. So although it may take a high initial current, that won't last long and it probably draws the right steady-state current for 3kW (and the accuracy of your resistance meter may not be wonderful).