If you are doing loop-in-switch you can run off a central JB. For example a 2G blank plate & backbox set just below the ceiling on each floor, with Wago etc inside.

Useful for testing, if a neutral required at each light switch, or loads of transformers. Can combine with Grid fish switch for em- lighting, etc.

Reply to
js.b1
Loading thread data ...

Quick 90 deg turns whilst pulling on the cable usually releases it. It's Helacon that I keep in the van so I have used them (just never used the box you linked to).

Reply to
ARWadsworth

Thanks, Adam and Andrew, for the replies. I obviously didn't have the technique right.

Reply to
mike

I was thinking the same thing but with the added theory that the existing light was pinching an earth from another circuit.

Reply to
ARWadsworth

I'm sure I remembered hearing that if an electrician does *any* work on a house that has deficient earth bonding, that work *must* be done at the same time otherwise no work can be done at all.

So the "missing earth" isn't necessarily in the light, it might be that the water pipes/gas pipes are not bonded. As indeed mine are not; I really need to get onto that.

Neil

Reply to
Neil Williams

I wondered about that, but would that really matter? Obviously, borrowing a neutral is bad practice - and likely to cause all sorts of problems if the circuits are RCD protected. But aren't all earths effectively connected to a single point anyway?

Reply to
Roger Mills

They are, but the practice is still frowned upon for various reasons... some include: If you have disconnected one circuit in its entirety while working on, it opens the possibility that an earth fault on an unrelated but "borrowing" circuit could place dangerous potentials on the disconnected circuits CPC. Also the CPC for the circuit is sized to provide fault protection for that one circuit - not more than one circuit, and possibly not even that rating of circuit (depending on what you borrowed from where). You also make testing and diagnostics on the source circuit more difficult since you may have introduced additional return paths to the main earth terminal.

Reply to
John Rumm

Yup, if the main equipotential bonding is not to current standard, then that would need to be rectified when carrying out any other work. Hence another case where a customer may refuse to pay for additional work, and the electrician is forced to turn down the job.

See:

formatting link
So the "missing earth" isn't necessarily in the light, it might be

Reply to
John Rumm

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.