My usual server is off line, so I cannot find the original thread..
Today the VRC 470F was delivered, so I got stuck in a removed all of the old controls and fitted the VR 65 and VRC 470F - this after getting house and water to a good temperature, in case it took longer than expected.
I had it all ripped out and new back in, within 3 hours. CH was obviously working fine, but not so sure about the HW side. CH now runs much more gently, modulates output down to minimum instead of the near flat out or off as before, boiler never seems to exceed 50C, so well inside condensing range.
I had VRC 470F running on its batteries for several hours, without the boiler etc. powered and it retained it time and date just fine. Maybe because the clock is in the 470F and is maintained by the batteries, your 470 has no battery rather it is powered from the ebus. Power the boiler down, no ebus power, clock is lost, but the settings are in non- volatile memory?
The HW issue...
I configured the boiler to assume a mid position valve, but it seemed not to make any difference other than the boiler then allowed me to set a max temp for the HW, but only a max of 50C. Before changing the control system, I was able to set a max boiler output temp of 75C.
470F Menu> Installer Level> System Config.> seems to suggest a Flow Temperature Target 40C, though I have seen this show 51C. It does not allow it to be changed..
There was a 'desired HW temp' setting in the 470F which could be set to a max of 70C.
I initially had the HW running on its cylinder stat. and it never seemed to try to heat the HW, maybe because it was already well over
50C, but I never saw the valve move at all.
I then swapped from stat., to the NTC sensor. I was than able to see the HW cylinder temperature on the 470F, it seemed to be just maintaining a constant 50C, but not much HW was consumed today so I cannot be sure, but I never saw the valve move to HW or the mid position. Except by pulling the NTC out of the cylinder insulation and allowing it to cool, did cause the valve actuator to move.
HW Boost didn't seem to do anything.
I wonder if the legionella setting, once per day might overrule the boiler, if it is the boiler holding the temperature down.
I set the clock deliberately 5 minutes fast, to see if the DCF77 receiver corrected it, as there doesn't seem to be any indication of reception. It hasn't corrected it yet, maybe over night reception? That is probably in the remote outdoor sensor and the 470F is showing the correct outdoor temperature.
For anyone interested - Boiler is a Vaillant 418 ECOfit Pure, valve actuator is a Sunvic SDM 1901.
Vaillant have been downright unhelpful (three times), when asked if the VCR 470F + VR65 + my boiler would work properly together. It seems they do, if I can solve the HW issue.