Heat Store Dilema - Dropping C/H temp.

Jun 13, 2022 Last reply: 4 years ago 2 Replies

The multi-fuel heat store turned up and I've been busy these last 2 weeks chopping out and adding pipes etc but now have a slight confusion.



The bedroom radiator circuit was originally fitted with larger radiators in each bedroom to enable sufficient heating with combi. running at UFH temp. and lower weather compensated to a max. of 55 degrees.



So now I have the heat store which opetates at 75 degrees which as far as I can tell won't have any stratfication so UFH manifolds and Raditors will all by supplied with 75 degree water.



UFH will sort it's self out correctly although I'd prefer to only supply them at 55 degrees; but I fear the bedrooms will overshoot before TRV's wake up so considering adding a thermostatic blending valve on the C/H flow from T/Store to drop it all down to 55 deg.C. The confusion I have is, will 2 pumps be required?



The cylinder is already pre-plumbed and supplied with a boiler pump for use with "heat only" boiler but I'm presuming an additional pump will be required on the C/H side of a mixing valve? If so then I guess I could fit a system boiler rather than a heat only boiler and re-purpose the supplied pump to circulate C/H feed downside of a blending valve?



Perhaps I'mm overlooking something or overcomplicating things?



Cheers - Pete


I don't have much experience with these things, but my understanding is that you shouldn't run UFH at 75C because of the risk of scalding, so it should be blended down at the UFH manifold. There is typically an additional pump to move water through the blending valve, because there is some recirculation of the water in the UFH (in other words it doesn't all return to the boiler, some of it goes around again, mixed with fresh hot water. There isn't a cold water input like in a shower, the 'cold' comes from the return loop).

AIUI you need that pump to pull in both hot and 'cold' through the mixer, because if you tried to push from the boiler end it wouldn't draw any water through the cold side.

If you want to run the boiler output at 55C, could you perhaps put the thermostatic blending on the output of the TS, ie before the UFH manifold? Then you're distributing 55C water around the place, which is suitable for all your emitters. When you run your back boiler the input to the TS will be hotter (and so the TS will store more energy) but the mixer will make sure the emitter temp doesn't get too high. You'd have to do the calcs to work out if the heat storage at 55C would be enough. (I don't recall why you went for a TS in the first place - was it intermittent heat sources like the back boiler or solar?)

The problem with a thermal store and a low temperature heat input (highly modulated boiler, heat pump, etc) is there's always some deltaT between the heat of the thermal store and the output of the hot water loop - means you can't modulate down to the most efficient level. It's likely not too much of a problem for a boiler, as long as you're prepared to run things that deltaT hotter (which you might need to if you want to store more heat).

Pass. I suppose you still need a pump for the cold side of the mixing valve, but I don't know if the one in the boiler would be suitable.

Not sure, I'm not very familiar with this area and probably missed something.

Theo

Indeed, I have 2 different UFH manifolds one old and one added for the 3 room extension 5 years ago. Both do their own blending with pumps and mixing valve but should the thermostat/mixing valve go dodgy I wouldn't want to supply them with 70 degree water to go around the UFH zones. Original zones are under chipboard/engineered wood and new zones are pipe in screed.

The TS has to be maintained at 75 degrees to give enough heat transfer to DHW which comes from rising main, through a coil in the top part of the store then out through a blending valve to take it back down to 60 degrees so reducing the store temp would reduce DHW "capacity".

I went for a thermal store as I'm adding a smallish wood burner with boiler (4.9kW to water, 3.4kW to room) to the lounge which I'm thinking if the gas boiler has bought the house up to temp by early evening the wood burner may well manage to maintain temp. for most of the evening; plus I have the option of adding Solar Thermal for summer DHW. And... I'm fed-up with the "all eggs in one basket" of a condensing combi-boiler that I regularly had to repair more-so into it's older years.

<snip>

After re-visiting things today, I'd forgotten the extra pump. The TS has

3 pumps already. One on a blending "manifold" made from 28mm copper + valve etc for the wood burner circuit; 1 pump for boiler circulation and one pump for C/H circulation, in which case I can add a blending valve between TS and CH pump which means ALL C/H water can go to all zones at a more suitable temperature. Just got to get a blending valve now and re-plan the pipework.