Ebay...
- Robin insulation tester w/continuity test
- Megger rcd tester
Make up...
- Your own wandering lead re R2 figures
You do not need an EFLI (Earth Fault Loop Impedance) tester, you can calculate Zs from Ze (based on supply type limits) + measure R1+R2. Unless you have a big welder or large HVAC unit Zs will not likely be a proble - more important to verify ring/radial continuity and then resistance is within limits re any bad connections.
If you DO buy an EFLI meter - 1) the non-trip type use a 15mA test current which will not test corroded armour or steel conduit continuity adequately (in my view only!) 2) the high current tests use
20-21-25A which will trip an RCD which requires bridging of the RCBO/ RCD.
On balance bothering with an EFLI tester is not important enough. Far better to do the IR & Continuity + RCD tests, if you use a lot of power tools & particularly hedge trimmer I would consider an RCD tester pretty essential. Fluke SM300 will at least test RCD operation
- it's just a resistor to cause a 30mA nominal leakage, it does not confirm trip trim like a proper tester.
Individual tools are good in that if something fails the replacement is confined to that tool - repairs can a) be a con re badly done b) be as much as a new machine certainly on Ebay. Multifunction tools are favoured because they can record for download later, direct into forms and so on.
Realise the limits of an IR tester. Air is a perfect insulator - thus the most grotesquely rotted TRS etc cable will pass quite happily despite rubber hanging off :-) That is why visual inspection can be "everything" and why I take IR as a "well it tells me someone trapped a cable in a floorboard by badly done notching. The best tester is the RCD tester - Socket and See do some quite cheaply on Ebay, but I prefer Megger RCDT320. They can be rebadged by electrical factors and thus very cheap because "it doesn't say megger on it", but is the exact same machine.
If you have an earth rod, that requires a specialised tester - which it is useful to have (although cheaper to put a shed on wooden sleepers and not use Class-1 tools outside :-)